I think the AC meter clamp test from Maine Sail will be interesting.. If the intermittent issue is from being close to a threshold, I think you would be able to measure that as long as the instrument can read resolution in the ma range.
Little bit interesting to note how those instruments work. When you run current through a wire, it creates a magnetic field and the clamp instrument measures that magnetic field.
So if you just clamp on the black wire, it that would indicate how much current the boat is using.
If I have two wires running next to each other and the currents are in opposite direction and in phase, the magnetic fields cancel each other so you measure zero current. If one of these wires now has slightly less current, the magnetic fields dont exactly cancel so what you are measuring is the difference in current between the two wires. So if you clamp on the black and white wires, the current in each should be opposite and identical and you would read zero. But if there was some leakage either to the green wire or somehow to the water, the black and white would not have the same current and you could read this.
Since the instrument is just reading magnetic field inside the clamp, if the sum of currents going one way is equal to the sum of currents going the other way, the instrument will read zero current. The interesting thing about this is that you can have a ground faul where half the return current is on the green wire and half on the white which is a really bad ground fault but the clamp meter around all three wires reads zero. At a marina, someone would just clamp on all three wires (easiest) and while this wont tell you if the green wire has current on it, measuring any current on all three wires means that the leakage is going into the water. (safety issue).
Clamp on black only - this tells the AC current draw of the boat
Clamp on black and white only If this is zero, you have no leakage and no problem.. If its not zero, you have leakage and its above the GFCI trip level, trips.
Clamp on green only. If you measured leakage on the black and wire wires but no current on the green wire, the leakage current is going into the water. If the leakage current is on the green wire, the reading for the black and white wire couple should equal the current on the green side.
Clamp on all three wires. Zero current only means that you dont have current leaking into the water. If you do have current leaking into the water, the clamp on all three wires will measure this. But.. you can have a ground fault leaking current to the green wire in the cable and you can not measure this with the clamp on all three wires.
And.. I could have something wrong in there. What you measure will be interesting..