Regarding the new regulator that I have purchased, I performed a water column test per @Ralph Johnstone in post #11.
That's just too fancy a setup you've got there.
The results varied a bit on multiple tests, and so did the temperature of the tanks vary during testing.
Much of the reason for most of that almost 2" error is the attraction of the water to the vinyl tubing, almost like friction. I should have mentioned to add a drop of liquid dish washing soap to smooth things out. As you say, the new reg. is set to 11".
Tank temp. wouldn't change the reg. output pressure as you've showed with your test of both the 10 PSI input (throttled tank valve ?) and 145 PSI input to the reg. producing the same output.
The next leak test I did was with the stove burners and oven shut off, but with the solenoid valve turn on. At this point, the input pressure gauge read 0 psi,
Now I'm lost ........... how can the input pressure to the reg. be 0 PSI (am I right here ?) if your propane tank is full. Did you have the tank shut off valve closed ?
the input pressure gauge read 0 psi, and my propane alarm inside the salon went off. This indicates a propane leak that is inside the boat.
Just because the tank showed empty because the valve showed 0 PSI, why does the propane alarm sound off. What is its sensor looking at to tell you there is a leak. inside the boat. I thought those things worked on a propane sniffer. But what do I know ? My propane system has no safety sensors. Just light a match and hope for the best each time.
I am confused as to why the input pressure gauge read 0 psi,
You're confused. How do you think the rest of us feel ?
It sounds as if the system initially had pressure to the reg. and then it went empty. Any chance you were venting large amounts of gas and the tank is now empty ? Or as I had previously mentioned, did you vent all of the gas overboard ? Is your supply the 1# tank or your 10# tank.
I am going to see if it also reads 0 psi if I disconnect the hose to the solenoid valve and let it vent to the atmosphere. Maybe this will give me a clue as to what is happening.
May I suggest you remove the reg. from the investigation and leave it where it is and just take off the pressure gauge AFTER you have ensured the tank valve is closed ? Crack open the tank valve and if there is any pressure in the tank, you will hear it, feel it, and smell it immediately, indicating the gauge is kaput ! OR, maybe the valve is stuck in the closed position e. Remember to tape and replace the pressure gauge when finished.
Now I seem to have leak somewhere in the salon near or in the stove.
Once again, may I suggest a simple bleed down test once you get things straightened out back at the tank and a guaranteed supply of gas at 11".
- Open all cabin openings (hatches, ports, etc.) in case there is a great bloody line leak which could prove embarrassing.
- Ensure all burners are shut off.
- Open the gas valve at the tank.
- Open the solenoid valve.
- Shut off the tank valve tightly.
- Watch the pressure gauge over the next few hours or overnight if you're OCD like myself.
- Any pressure drop indicates a leak downstream of the tank shut off valve.
- If you have a leak, your nose is probably the best detector.
- If you have no sense of smell, a squeeze bottle with a few drops of soap detergent is your next best opetion.
This is day four of dealing with this problem, and I have found that the most difficult problems are those where there are multiple failures.
Just saw your update edit :
The input pressure read 0 psi and I could feel a slight supply of gas from the end of the hose.
Maybe problem here :
Yes, an 11" reg. output of propane is about as strong as a fart on a quiet night. HOWEVER, if the tank valve was wide open, the gauge must show full tank pressure at all times. It has a huge supply capacity due to its high pressure. If not, something is not right in the tank valve.
If I put my finger over the end of the hose, the flow decreased and the input pressure gauge increased to about 100 psi.
This means the tank valve was only pertly open or the tank valve is partially plugged.
I will now wait to get my air compressor and I'll pressurize the system and try to locate the leak inside of the boat.
See the bleed down test above. Faster and simpler.
I find this problem most interesting because it's NOT on my boat. On my boat it'd be a whole 'nuther problem.
Let us know what you find.