I will check when I am on the boat tomorrow.Make sure that the "Switch circuit function" is not set to "enable" , as it will turn off the battery. Go to settings on your suspect battery and you will find it about half way down.
I don't see anything wrong.I don’t want to hijack @SycloneDriver’s post, but this is AlFP system related, so hopefully not egregious… if I should start a new thread, please comment,
I was checking my new Humseink LifePo4 batteries today after the batteries have been on the charger for a few days. Batt 1 showed 100% SOC and Batt 2 showed 99%. Interestingly, the BMS on Batt 1 shut off the charging switch. I assume since it was at 100% and couldn’t accept any more charge. The batteries are paralleled (see photo below).
View attachment 233092
I went out for a 2.5 hour sail today, with a light load on the house bank (fridge, VHF, stereo, CP & instruments).
When I got back, I left the charger off until I could check the BMS for the 2 batteries. Now, Batt 1 still showed 100% SOC and batt 2 was at 86% SOC.
I am not sure why these batteries, if wired in parallel, would not supply power to the house system in equal measure. Instead, it seems that one battery is doing all of the work
View attachment 233093 View attachment 233094
I have written to Humseink to see what they can tell me (if anything). I have discovered that their BMS app will not let me see what the individual cells are doing. They did say that their engineers are working on an upgrade to the app.
So, here is a crude drawing of my DC system (left out the AC side of the equation for now)...and only the house side. Left off the starter battery, switch, charger, etc for that.
View attachment 233095
Does anyone see anything blatantly wrong with this set up (I hope not, as I have sailed with it a few times now). Or could this just an issue with the batteries? One thing I could try is to install a positive and negative bus bars and hook each battery individuslly to the bus bars. But the charger would charge the bus bars (single output charger ). Not sure that changes things much. Does paralleling LFP batteries need to be different than FLA?
Greg
This can happen when the individual cells in a battery are not balanced. The BMS will continue accepting a charge until all the cells are balanced at (or very close to) the same voltage. In use the cells will not charge or discharge evenly, top balancing returns them to equal voltages. This is pretty normal behavior for LFP batteries.I was checking my new Humseink LifePo4 batteries today after the batteries have been on the charger for a few days. Batt 1 showed 100% SOC and Batt 2 showed 99%. Interestingly, the BMS on Batt 1 shut off the charging switch. I assume since it was at 100% and couldn’t accept any more charge. The batteries are paralleled (see photo below).
Hi Troy,I don't see anything wrong.
I am curious as to what you have the charge and maintenance voltages set at in the charger?
Does the alternator have a programmable regulator?
Thanks Dave,This can happen when the individual cells in a battery are not balanced. The BMS will continue accepting a charge until all the cells are balanced at (or very close to) the same voltage. In use the cells will not charge or discharge evenly, top balancing returns them to equal voltages. This is pretty normal behavior for LFP batteries.
The other problem, uneven discharge between the 2 batteries seems more unusual. It may take a few charge/discharge cycles for the BMS to learn the SOC. The usual causes for the imbalance between the 2 batteries are uneven jumper lengths or the manner in which the batteries are put in parallel. The way you have wired the batteries was once the recommended method, it is still fine, however, current thinking has the batteries connected to a bus bar to parallel them and the loads taken off the bus. Buried somewhere on the Victron site is a basic wiring manual that shows the different methods of paralleling batteries. There may also be information on Calder's site, www.BoatHowTo.com.
While we're looking at the photos, the DC+ wires all need to be fused. One of the dangers of LFP batteries is the amount of current they can discharge in a short time. There should only be 2 DC+ connections on the battery, the jumper from B1 and B2 and the cable to a Class T fuse. A Class T fuse should be used because it has a higher interrupt level (AIC) than other fuses. If there is a short the power delivered from an LFP battery can arc across a blown fuse. Class T fuses prevent the arcing. All the wires after the Class T fuse can be fused with other styles of fuses. ATC fuses in inline holders or a Blue Seas fuse box will work. The fuse box is a bit neater.
”Bulk” is not a voltage setting. It is maximum current that the charger can apply. With a discharged battery, the voltage at that current will initially be below the absorption voltage setting. As the battery SOC gets higher, its voltage will rise. Once the programmed absorption voltage is reached the charger will reduce the charge current so as not to exceed the absorption voltage setting.It doesn’t say what the “bulk” setting is. I think it is around 13.5 or so.
I'm not familiar with that brand of battery, but 13.2V is too low a float voltage for lifepo4 chemistry.... ideally 13.5-13.8V. In the case of lithium, absorption = bulk........ I also need to add a DC to DC charger.
I have reprogrammed the charge and float settings on my Pronautic P1230 charger. I set it at 14.2 charge and 13.2 float. I verified that it stopped charging when the battery was full.
The alternator is presently connected to both the house and start battery though an isolator. With the charger on and the engine running the charge current was at about 45 amps. I ran the engine for about 5 minutes at cruise rpm and the alternator barely got warm. The charger is only connected to the house battery. It pumped out 30 anps for hours, it got very warm.
...
GregI was checking my new Humseink LifePo4 batteries today after the batteries have been on the charger for a few days. Batt 1 showed 100% SOC and Batt 2 showed 99%. Interestingly, the BMS on Batt 1 shut off the charging switch. I assume since it was at 100% and couldn’t accept any more charge. The batteries are paralleled (see photo below).
View attachment 233092
I went out for a 2.5 hour sail today, with a light load on the house bank (fridge, VHF, stereo, CP & instruments).
When I got back, I left the charger off until I could check the BMS for the 2 batteries. Now, Batt 1 still showed 100% SOC and batt 2 was at 86% SOC.
I am not sure why these batteries, if wired in parallel, would not supply power to the house system in equal measure. Instead, it seems that one battery is doing all of the work
View attachment 233093 View attachment 233094
I have written to Humseink to see what they can tell me (if anything). I have discovered that their BMS app will not let me see what the individual cells are doing. They did say that their engineers are working on an upgrade to the app.
So, here is a crude drawing of my DC system (left out the AC side of the equation for now)...and only the house side. Left off the starter battery, switch, charger, etc for that.
View attachment 233095
Does anyone see anything blatantly wrong with this set up (I hope not, as I have sailed with it a few times now). Or could this just an issue with the batteries? One thing I could try is to install a positive and negative bus bars and hook each battery individuslly to the bus bars. But the charger would charge the bus bars (single output charger ). Not sure that changes things much. Does paralleling LFP batteries need to be different than FLA?
Thanks. I was looking for something in the literature. I guess it runs at 20 amps (max for my charger).”Bulk” is not a voltage setting. It is maximum current that the charger can apply. With a discharged battery, the voltage at that current will initially be below the absorption voltage setting. As the battery SOC gets higher, its voltage will rise. Once the programmed absorption voltage is reached the charger will reduce the charge current so as not to exceed the absorption voltage setting.
Looking at your screenshot it appears battery 2 has its discharge FETs off, even though the app is reporting they are on. Notice the difference in voltage (13.15V vs 13.38V). You can have small differences in reported voltage with paralleled batteries but not that large. Can you cycle the discharge FET switch? Maybe that will reconnect it.
Thanks for the tips on the alternate BMS software. I tried a few (I don't think I tried Solar Overkill)..none of the alternates really did much. I will try your favorite tomorrow when I get to the boat.Greg
On the RV forums I subscribe to, several campers with 2 LiTime batteries were experiencing similar. Basically, one battery was going into "standby" while the other carried the load. There were various "fixes" suggested by LiTime which included taking both batteries to zero, and then resetting. Nobody wants to take LFP batteries to zero for fear of never being able to wake them again, especially on a boat.
Bottom line: it's a BMS software flaw that eagerly shuts down one battery of a parallel combo. I wonder if your battery set is using the same BMS as LiTime.
Solutions:
- download and try Solar Overkill app on your phone. This may allow Bluetooth access to more BMS functions and information. I prefer the Solar Overkill app because I know the software is being maintained. I have a Techcella battery I bought 3 months ago that has disappeared from the market, so I have no hope of the OEM app being updated.
- cell balancing on a regular basis is critical in a parallel environment
- follow factory instructions on recovery. But in LiTime's case the problem reoccurs regularly.
- go to single battery ops, either buying a larger battery or using existing batteries one at a time and switching between them. If you keep 2 batteries at any significant difference in SOC, you CANNOT parallel them.
- I went with a single larger (160AH) battery because in both personal experience and electrical engineering I have learned that paralleling batteries - regardless of type - is inherently unstable because no 2 batteries are perfectly matched. Nobody wants to talk about this until something goes wrong. And there are many, many users of paralleled batteries where nothing has ever gone wrong. In my case it was a battery fire with lead acid batteries (no BMS except me to shut things down). Others have experienced what you are going through.
- I have had many, many people tell me I'm wrong and don't know what I'm talking about. But whenever the voltage is the SLIGHTEST bit different between the 2 batteries, they will try to equalize the voltage, often with tremendous currents depending on wire size, voltage difference, and internal battery resistance. That's why the parallel configuration requires attention to details of wire lengths or placement of bus bars at equal distance from the batteries. And correct fusing. The BMS in an LFP battery is the last line of defense to protect the battery when things go wrong.
Fred W
The batteries should be charged independently before being placed in service and after winter storage. Using the Victron charger plug it in and let it run until the BMS shuts down the charging. This may take a pretty long time. Don't use or parallel either battery until both are fully charged and the BMS has shut down charging. The SOC may show 99% or 100% while the BMS stays in the charge mode, this is due to both rounding errors and the individual cells not being balanced.A little confusing but I will separate the 2 batteries and charge them separately for a few days to see if I can get them to within 0.3 volts difference.
This really isn't an issue with a 2 battery system wired in the manner you have wired yours. It is a problem if both + and - come from the same battery with the second battery attached to the first.Typically, when batteries are connected in series or parallel, the battery closest to the load's positive and negative terminals will be consumed first.
Is the communication between the BMSs on your 2 batteries? I think this is a bunch of hogwash on batteries with internal BMSs especially if there is no communication between the two BMSs. A single external BMS that manages several batteries in a bank may do this, but not independent BMSs without the ability to communicate with the other batteries. On my 3 battery parallel bank the batteries are always in the same state, (charging, discharging, standby) and the charging current is evenly divided between the 3 batteries because the cables are all the same length and they all started independently charged and balanced.This behavior is not standard in parallel systems, but is intentional in “smart” battery design. We use advanced BMS algorithms to manage load distribution based on real-time conditions.
Thanks Dave,The batteries should be charged independently before being placed in service and after winter storage. Using the Victron charger plug it in and let it run until the BMS shuts down the charging. This may take a pretty long time. Don't use or parallel either battery until both are fully charged and the BMS has shut down charging. The SOC may show 99% or 100% while the BMS stays in the charge mode, this is due to both rounding errors and the individual cells not being balanced.
This really isn't an issue with a 2 battery system wired in the manner you have wired yours. It is a problem if both + and - come from the same battery with the second battery attached to the first.
Is the communication between the BMSs on your 2 batteries? I think this is a bunch of hogwash on batteries with internal BMSs especially if there is no communication between the two BMSs. A single external BMS that manages several batteries in a bank may do this, but not independent BMSs without the ability to communicate with the other batteries. On my 3 battery parallel bank the batteries are always in the same state, (charging, discharging, standby) and the charging current is evenly divided between the 3 batteries because the cables are all the same length and they all started independently charged and balanced.
So, take the batteries home, put each of them on the charger and try again. You might want to ask the company how to read the cell voltages. Without being able to read the cell voltages there is no way to confirm the batteries are top balanced.
A great learning experience.I guess I know what you get for $139.
GregThanks Dave,
I did charge them independently before I took them out to the boat. But I will try that again. I don't know if they were both in "Storage" mode when I switched the charger to the other. Maybe that is why I have some difference in the 2 batteries. ..
The part about the BMS's talking to each other (from Humseink) is the part I find confusing. I was not aware that these 2 batteries would talk to each other and decide which one is providing the juice... and which one is taking it easy. Seemed a bit far-fetched to me.
I will re-balance them again over the next few days (I am probably not bringing them home...but will disconnect one at a time and let the charger do its thing over night for each battery.
I did ask about seeing the cell voltages. They said the APP doesn't do that (yet), but they are working on a new release... so who knows.
I guess I know what you get for $139.
Greg
I don’t want to hijack @SycloneDriver’s post, but this is AlFP system related, so hopefully not egregious… if I should start a new thread, please comment,
I was checking my new Humseink LifePo4 batteries today after the batteries have been on the charger for a few days. Batt 1 showed 100% SOC and Batt 2 showed 99%. Interestingly, the BMS on Batt 1 shut off the charging switch. I assume since it was at 100% and couldn’t accept any more charge. The batteries are paralleled (see photo below).
View attachment 233092
I went out for a 2.5 hour sail today, with a light load on the house bank (fridge, VHF, stereo, CP & instruments).
When I got back, I left the charger off until I could check the BMS for the 2 batteries. Now, Batt 1 still showed 100% SOC and batt 2 was at 86% SOC.
I am not sure why these batteries, if wired in parallel, would not supply power to the house system in equal measure. Instead, it seems that one battery is doing all of the work
View attachment 233093 View attachment 233094
I have written to Humseink to see what they can tell me (if anything). I have discovered that their BMS app will not let me see what the individual cells are doing. They did say that their engineers are working on an upgrade to the app.
So, here is a crude drawing of my DC system (left out the AC side of the equation for now)...and only the house side. Left off the starter battery, switch, charger, etc for that.
View attachment 233095
Does anyone see anything blatantly wrong with this set up (I hope not, as I have sailed with it a few times now). Or could this just an issue with the batteries? One thing I could try is to install a positive and negative bus bars and hook each battery individuslly to the bus bars. But the charger would charge the bus bars (single output charger ). Not sure that changes things much. Does paralleling LFP batteries need to be different than FLA?
Greg
I can turn off charging and discharging. My battery does not have heat. I am not sure what “Forced Hibernation” does.What screen pops up when you touch "BMS Control" on your app?