Thank you Mainesail
I'm glad you pointed it out as I did not take that into account in my calcs, I think I have a good grounding of the levels with regards to battery maintenance and definitely do not want to kill them
I'm off to the boat to carry on with cleaning up the PO's mess. Look forward to all replies.
(I'm happy to purchase a small genset also)
Some other thoughts but typing from the phone is not easy.
#1 Peukert! You will not get anywhere near the 450/225Ah's when running a 100+amp load. Those batteries are rated using an 11.25 A load. Any load higher than 11.25A will drastically reduce the number of usable Ah's. My guess is that you'll actually have less than 80Ah's usable, if that, with a 100+ amp load. Even if your alternator contributes a full third of the power you're still a solid 4-5 times beyond what the batteries Ah capacity was rated at.
#2 Inverter efficiency: With an AC you may find you're only getting 80-85% efficiency, if that.
#3 AC Startup. You'll need a big inverter than can handle big in-rush to start the AC when it cycles. You'll then hope that the batteries don't trip the inverters low voltage shut down when the voltage dips.. Every cycle of the AC could be equal to the current needed to start your engine. With a small boat AC's cycle frequently. These start ups could be like starting your motor 15-25 times per hour..
#4 Alternator: You'll likely burn out your alternator as they are not designed produce full output for long periods of time. The full output will also not be 50A and more likely in the neighborhood of high 30's to low 40's when hot.
#5 Recharging: At some point you'll need to put all those Ah's back into the battery which can take 110-125% of what you took out to go back in. This is a LOT of engine run time on a small 50A alt.
#6 Engine: Running your engine lightly loaded for long periods of time, a 40A alt is lightly loaded for a marine diesel, is not the best practice and can lead to cylinder bore glazing. You'll want to run it real hard when not using it for AC requirements to remove any glazing that has begun.
#7 Generator: Unless you have a bank that is significantly larger than what you currently have, a generator is going to be your best bet.