Electrocution at Lake Pleasant, AZ

Feb 6, 1998
11,701
Canadian Sailcraft 36T Casco Bay, ME
Please correct me if I am wrong.
AC ground wire (green) is never connected to a ground point on the boat (engine, keel, etc.). The boat's AC system is grounded thru the green ground wire and into the marina shore power system.

This is definitely incorrect. AC GREEN/GROUNDING is always conencted to the vessels DC grounding bus but AC NEUTRAL/WHITE is never connected to AC GREEN? GROUNDING on-board the vessel when tied to shore power.

The ONLY TIMES AC GREEN/GROUNDING and AC NEUTRAL/WHITE are ever tied together on the vessel is:

- When actively disconnected from shore power and inverting power with an inverter (this is why MARINE SPECIFIC inverters are a MUST).
- When actively disconnected from shore power and generating power with an genset (this is why MARINE SPECIFIC gensets are are critical)
- If you have an isolation transformer powering your vessel.

For a 120V 30A system this acceptable wiring from the ABYC: (If the vessel is fitted with a reverse polarity indicator the "branch" brakers only need to interrupt the AC BLACK/HOT wire.)
 
Jun 21, 2004
2,782
Beneteau 343 Slidell, LA
Much thanks Maine. Will have to trace my AC system wiring. It was likely wired correctly from factory; however, I want to ensure that it was wired and grounded properly.
 

srimes

.
Jun 9, 2020
211
Macgregor 26D Brookings
Is there a simple leakage test that can be done with a basic multimeter? That would be easier and more robust that trying to trace all wiring on an old boat. Maybe check water voltage/resistance vs boat ground under all scenarios: everything off, shore power, inverter power, generator power.

This incident sounded bad enough that just dipping a toe in the water at the back of the boat would have given a shock.
 

walt

.
Jun 1, 2007
3,535
Macgregor 26S Hobie TI Ridgway Colorado
Is there a simple leakage test that can be done with a basic multimeter?
This sort of problem is exactly why ground fault detection (ie, GFCI and ELCI) exists. You can tell with a clamp on current meter on the power cord if you know what you are doing but the simplest way is to just use GFCI. Some marinas will have GFCI or ELCI already built into the power source and if you plug in and it does trip (and the ground fault detection is working - these always have a manual way to self test), you likely have some level of problem.

If the dock pedestal does not have ground fault detection (some do, some dont, the marina in this thread likely does not), just insert something like in the link below in the cord between the dock power pedestal and the boat. If it trips and doesnt allow power to the boat, you have some issue that needs to be addressed. If you get power and the instrument is working, you dont have a problem.

One example of a GFCI extension that would provide a quick and reliable test..
 
Last edited:

jviss

.
Feb 5, 2004
7,089
Tartan 3800 20 Westport, MA
This sort of problem is exactly why ground fault detection (ie, GFCI and ELCI) exists. You can tell with a clamp on current meter on the power cord if you know what you are doing but the simplest way is to just use GFCI. Some marinas will have GFCI or ELCI already built into the power source and if you plug in and it does trip (and the ground fault detection is working - these always have a manual way to self test), you likely have some level of problem.

If the dock pedestal does not have ground fault detection, just insert something like in the link below in the cord between the dock power pedestal and the boat. If it trips and doesnt allow power to the boat, you have some issue that needs to be addressed. If you get power and the instrument is working, you dont have a problem.

One example of a GFCI extension that would provide a quick and reliable test..
I have one of those, but it's not going to mate with a standard shore power cable without some adapters.
 

walt

.
Jun 1, 2007
3,535
Macgregor 26S Hobie TI Ridgway Colorado
Yep.. and some chance you have ELCI or GFCI correctly wired up on the boat which will also prevent this sort of problem. But then you still have the problem of ground fault not being wired correctly on the boat since this probably is often done by the owner.

Ground fault detection just lets you know there is a problem. The problem could be the AC hot wired to an underwater metal structure and be very dangerous, or it could be as simple as having the neutral and ground (white and green) connected together on the boat which is probably not dangerous, but may increase corrosion.
 
Apr 5, 2009
3,098
Catalina '88 C30 tr/bs Oak Harbor, WA
"...“The victim’s boat had an electrical connection system which was not compatible with the marina’s receptacle,” MCSO explained in a news release. “Electrical safety features were bypassed by the intentional and improper modification of the boat’s electrical connection system.”
Does anyone know what the modification was that caused this?
 
Jan 18, 2016
782
Catalina 387 Dana Point
Almost unbelievable people are killed for the lack of an ELCI/GFCI. Sure, the guys boat was wired wrong - which is wrong. But in a general sense, that may happen anyway (malice, ignorance or accident). Just like I may accidentally drop my hair dryer in my toilet. But ELCI/GFCI would have kept popping, but it would have saved lives.

IMHO Insurance should require it, and legislation should have a fixed time out for grandfathered installations. For private docks, the owner's insurance should require it. Nobody should be dying in water after ground fault protection was available at consumer prices.
 
Jan 11, 2014
12,749
Sabre 362 113 Fair Haven, NY
Is there a simple leakage test that can be done with a basic multimeter? That would be easier and more robust that trying to trace all wiring on an old boat. Maybe check water voltage/resistance vs boat ground under all scenarios: everything off, shore power, inverter power, generator power.

This incident sounded bad enough that just dipping a toe in the water at the back of the boat would have given a shock.
A clamp on meter will work. If there is no leakage the power the meter will register 0, if there is leakage it will show current passing through the cable. With AC the alternating current cancels the magnetic field so the meter reads 0, if there is leakage the current entering the cable is greater than the current leaving the cable and it registers current passing through.

Look at the photo in post #43, this is a clamp on meter showing almost 2 amps of leakage.