I am in need of suggestions for troubleshooting an apparent issue with my AC power on 2012 Hunter 39. The Line 1 main AC switch(immediately after the shore power connection in the aft cabin on the boat and not the main breaker on the distribution panel) is intermittently tripping. Meanwhile the line 2 connection remains energized and apparently functioning properly (AC units powered and running) Here is a long explanation of the circumstances...

This first happened two weeks ago following a heavy rain. I discovered the line 1 side of the distribution panel (batt chg, water heater, outlets, microwave) was dead. The line 1 switch in the aft cabin had tripped. All of the breakers on the distribution panel were in the on position and had not tripped. I attempted to reset the main line 1 switch and it immediately tripped. I turned off all of the line 1 breakers (main and subs) and then reset the line 1 switch. It held until I switched on the main breaker for line 1 on the distribution panel (all of the sub circuit breakers were off).

I checked the boat cord connections and the shore power pedestal (50amp/120v y'ed to 2 30 amp cords). When I separated the y to cable connection at pedestal, some water had pooled inside the marinco screw connection. There is no charring from loose connector/shorting and I assumed it may have been a ground issue caused by water. After drying out, I tried to reset switch... it still tripped. I left the boat frustrated and returned a couple hours later... the line 1 switch worked and power was restored. It has continued to remain powered until this past weekend when it again tripped. This time there was not rain and the y to cord shorepower connection did not have moisture inside. I waited a couple hours and the line 1 switch reset and power was restored.

Any suggestions for troubleshooting and finding cause??

For further background, about two years ago, the line 2 main switch in aft cabin would occasionally trip. I asked dealer about having it looked at and he indicated it was likely a problem with the marina shore power and leaking current from another boat. It happened a couple more times that summer and then has not occurred since. Now, a couple years later, it is happening again on line 1 main switch.

I've attached a picture of the front and rear of the line 1 / line 2 main switch apparatus should it help to show anything amiss. Thanks for any suggestions and advice.
 

Attachments

Feb 6, 1998
11,709
Canadian Sailcraft 36T Casco Bay, ME
Those are ELCI breakers and they trip on a 30mA imbalance between shore white and shore black. Your "Twist-Lock" shore power cordset and high start up loads causing an imbalance are the likely culprits...
 
Nov 15, 2009
29
Hunter 39 New Castle, NH
MaineSail:
Thank you. Is this something to be concerned about and/or is there anything I can/should do to prevent from tripping? I'm assuming the hot water heater and battery charger kicking on simultaneously, may be a culprit (the microwave and outlets where not in use at the time)?