Until the contactor welds or the control circuit gets fried by the over-voltage event...External BMS using contactors. Problem solved.
Mark
It is 100v. Solar panels put out high voltage low amp current. When panels are placed in series the voltages are added, so a 300w panel may have an output of about 50v at 6 amps, place 2 in series and the combined output is 100v at 6 amps. Higher voltages are used so that smaller gauge wire can be used. Panels are placed in series to get the higher voltage and to have one controller control multiple panels instead of one controller for each panel.100V or 100W?
you lost me at 100V solar panels
We could, but our computers don't run very well on whale oil.Can't we just go back to Kerosine? Or whale oil?
With a lead acid battery the internal resistance of the battery is high enough to reduce the voltage a bit. Applying 120v to a 12v battery will cause the battery to rapidly over heat and expell hydrogen gas which is explosive. This will happen at fairly low voltages, around 15 to 16vdc.he solar panel output is current limited and the voltage instantly drops to the battery voltage and dumps whatever current the solar panel puts out into the battery but this will never exceed the short circuit voltage of the solar panel.
That's only true until the battery reaches full charge and the BMS tries to interrupt the current. When the switch opens, the voltage rises to 100V instantly.On the lines of what colemj is pointing out, if you take a solar panel configuration with a 100 volt open circuit voltage and connect it to a 12 volt battery, it does not apply 100 V to the battery. The solar panel output is current limited and the voltage instantly drops to the battery voltage and dumps whatever current the solar panel puts out into the battery but this will never exceed the short circuit current of the solar panel.
An excellent point. A true high reliability system needs to incorporate mechanisms to *detect* when a fault occurs, otherwise redundancy is defeated.Nobody with these BMS's even knows if their MOSFETS are shorted or not until they tell the BMS to shut down and see if it does. Then when they turn it back on, they again have no idea if they are shorted now. You only find out a MOSFET has failed in your BMS when you find your battery ruined (as this case proves). Otherwise, it is all hope.
I am not arguing against such a solution. But Rodd's point still applies: you need to select / design said BMS to ensure it can withstand the highest voltage that may be present in your system - and interrupt the highest current while you're at it. I don't know about "no" compromises - coil current is a big one - but I do tend to trust mechanical disconnects a bit more than solid state.An external BMS and contactors are about as robust a system as can be designed, with no compromises, and allows one to take advantage of all aspects of their electrical system.
That's an overly broad and misleading statement. A MOSFET's stress level is a function of how the circuit was designed, not how fast it's switching. Thermal, environmental, and mechanical stress are all factors as well as electrical. The drive inverter in my EV has been flawlessly switching tens and hundreds of kW at 350V and >20,000 cycles/second for 13 years and 4000 operating hours while subject to all the extremes that come with an automotive environment in New England.I dislike MOSFET switches in critical power systems like a BMS. Even in an inverter, I prefer a line-frequency type over a high-frequency one because the necessary MOSFET's in them are less stressed. They are fine in solar controllers because those are rated for the voltages stated, and are usually embedded in giant heat sinks in open air.
That would definitely eliminate the fire hazard...Can't we just go back to Kerosine? Or whale oil?
With a lead acid battery the internal resistance of the battery is high enough to reduce the voltage a bit. Applying 120v to a 12v battery will cause the battery to rapidly over heat and expell hydrogen gas which is explosive. This will happen at fairly low voltages, around 15 to 16vdc.
However, a LFP battery has very low internal resistance and will not cause the voltage to drop significantly. The BMS can mitigate the high voltage and shut off charging. In the case Rod explains, the controller failed and the full 100v went to the battery's BMS, the MOFSETs couldn't handle that much voltage and failed allowing the battery to experience an extreme over voltage condition. The MOFSETs were rated at 60v (if I remember correctly, it's been a week since I watched the video), the 100v fried them.
I disagree with this, but I wasn't even thinking of switching frequency in terms of a unit's robustness. I was thinking of the large iron transformer in a line-frequency unit that can absorb a lot of stuff that can damage MOSFETs. Surges, motor LRC, power factor mismatches, etc. The tiny transformers in high frequency units are little help there at all.A MOSFET's stress level is a function of how the circuit was designed, not how fast it's switching.
This is correct as far as it goes. However, what you are missing is that not everyone has a single panel (100V 400W as in your example). Lots of people have multiple panels with multiple controllers, and even other charge sources running at the same time.Lets use an example of a 400 watt solar panel that is somehow 100 volts open circuit. Maximum current out of this 400 watt panel with a 100 volts open circuit might be about 5 amps (maximum power point voltage of 80 volts and 5 amps) The short circuit amp of this panel might also be about 5 amps.
When you apply that solar panel directly to a battery,. it can only put 5 amps into the battery. No more than this. What happens to the battery voltage if you put in 5 amps. Maybe it goes up .1 volts, maybe .3 volts.
Remember that the solar panel 100 volts is open circuit with no load or zero current. This is way different than a 100 volt power supply that can attempt to put out 50 amps at 100 volts.
In our case above, when the 400 watt solar panel example was put directly on the battery, the battery voltage might only increase by a few hundred millivolts.
This is how solar panels work.. They are basically a current source with an open circuit voltage limit.
FYI, google what the internal impedance of a 100 amp hour LFP battery is. I got 2 to 4 milliohm.
At 4 milliohm, that 400 watt panel with 5 amp short circuit current only raised the battery voltage by .02 volts. That will not cause a problem.
However, a 400 watt solar panel connected to a battery with no regulation (ie, the failed MPPT controller looked like a short between in and out) will cause the battery to over heat and damage itself if its left on for long enough. Most likley the battery cooked because there was no regulation on the charge long after the battery was full. The mystery is what is the BMS supposed to do if the battery is being overcharged because regulation was damaged.
You cant think of a solar panel as a fixed voltage source since its not even close to that.
Yes.. The point earlier is that a solar panel might have an open circuit (no load ) voltage of 100 volts but it will not put out more current than its short circuit spec which is usually close to the maximum power point current. A solar panel looks like a constant current source over much of its operating voltage range and when connected to something like a battery that is below the open circuit voltage, the panel just injects near is short circuit current into the battery and this generally will only result in an initial voltage rise of the panel current times the internal impedance of the battery. Lets even go to an 800 watt panel (it was on an RV) with an open circuit voltage of 100 volts and a short circuit current of 10 amps. 4 milliohm battery impedance results in the initial battery voltage increase of a small 40 mv. Not damaging.That's only true until the battery reaches full charge and the BMS tries to interrupt the current. When the switch opens, the voltage rises to 100V instantly.