DC induction cooktop

Feb 16, 2021
544
Hunter Legend 35.5 Bellingham
Does anyone recommend a specific induction cooktop setup? I’d prefer to go DC for efficiency, but am uncertain of pitfalls to this approach. Would AC be better? My current setup is 460ah of 12v wet cell battery bank. Inverter is a West Marine 15 WCU-15 model 288 524
  • Continuous output: 1,500 VA
  • Surge: 4,000 VA for 15 seconds
  • Waveform: modified sine wave
  • Efficiency: 85% full-load, 92% peak
  • 12V charger: 75A, three-stage
  • Low-voltage cutoff: 10.0V
 

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
I would go AC.
You will have a lot more choices in the models available to buy.
Depending where your batteries are the cabling and fusing alone for a 12VDC circuit could get pretty expensive to do.
You still have some limits with the 1500W inverter - a lot of them go to 1800w.

I have slowly been making the conversion.
The propane stove is still there but hasn't been used at all in several years, the oven unused probably 5-6 years.
Bread machine, rice cooker, instant-pot, tea kettle, coffee pot, probably other electric galley gadgets I can't think of right now.
The instant-pot gets used a lot more than the stove top induction unit.
Only thing I will miss is the BBQ, but I can live with that.

A couple years ago I installed a pair of 12V 460AH Epoch LifePo4 batteries and that made the final decision for me.
Magnum 2812 charger/inverter.

There are some pretty lengthy and informative discussions about electric galleys at cruisersforum and sailnet so look over there too.
 
Last edited:

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
This is the summary from Gemini AI about pulsing vs. continuous power induction units.

Side-by-Side Comparison
FeaturePulsing Control (Budget / Entry)Continuous Current (Premium / Chef-Grade)
Heat DeliveryOn-Off Square Wave (Full power / Zero power)Uniform, constant, modulated wave
The Simmer TestCycles between aggressive boiling and doing nothingSoft, unbroken, consistent tiny bubbles
Noise ProfileAudible "click-buzz-click" at low settingsSilent operations (aside from normal cooling fan)
Off-Grid EfficiencyLess efficient due to rapid electronic switching lossesHigher efficiency (~94%); draws a clean, predictable line
Vessel ForgivenessRequires heavy cast iron/clad pans to buffer the pulsesWorks flawlessly even with lightweight magnetic pans
 
  • Like
Likes: skunther
Sep 30, 2016
437
Island Packet IP 44 Ventura, CA
This is the summary from Gemini AI about pulsing vs. continuous power induction units.

Side-by-Side Comparison
FeaturePulsing Control (Budget / Entry)Continuous Current (Premium / Chef-Grade)
Heat DeliveryOn-Off Square Wave (Full power / Zero power)Uniform, constant, modulated wave
The Simmer TestCycles between aggressive boiling and doing nothingSoft, unbroken, consistent tiny bubbles
Noise ProfileAudible "click-buzz-click" at low settingsSilent operations (aside from normal cooling fan)
Off-Grid EfficiencyLess efficient due to rapid electronic switching lossesHigher efficiency (~94%); draws a clean, predictable line
Vessel ForgivenessRequires heavy cast iron/clad pans to buffer the pulsesWorks flawlessly even with lightweight magnetic pans
Well thanks a lot. I was perfectly happy with my pulse control induction burner. Now Im lusting after a Breville Control Freak continuous current type. I didnt know that was a thing.
 
Sep 30, 2016
437
Island Packet IP 44 Ventura, CA
OP, You want AC for induction. Your inverter should be able to power a typical single burner induction cooktop. When Im running a 1800watt induction burner its pulling a little over 10 Amps AC and about 110 Amps DC from the battery. The math seems a little funny on that, but thats what my display is showing, and close enough for planning.
 
Jun 17, 2022
539
Hunter 380 Comox BC
There are also mid-grade (semi-commercial) cooktops that will vary the output 800-1800W and use a switch mode below 800W. Changbert is one of them.

I'd stay away from Salton .... Costco had them for a while and they had a high return rate.

I'd stick with an inverter. The inverter is likely very close to the batteries, so you only need 2-3 m of very large capacity conductor and the large fuses serve many purposes. If you go DC, you'll need large conductors (high current) all he way to the hob. This is both expensive and generates high loses due to voltage drop under the large current draw. AC (higher voltage) is much more efficient, even with the small inverter loss.

Our Victron inverter (3000/120) doesn't blink an eye running the 1800W / 120V induction hobb.
 

dLj

.
Mar 23, 2017
5,095
Belliure 41 Back in the Chesapeake
I’d prefer to go DC for efficiency, but am uncertain of pitfalls to this approach. Would AC be better?
OK, so I'm not, obviously, well enough versed in the actual units - but I don't understand this question. Induction heating is, by definition, done with AC power. The unit on the stove top must be using AC to heat the cooking pot/pan/whatever.

Induction heating accomplishes it's heating capabilities via a rapidly oscillating magnetic field what causes the ferro-magnetic material of your pot/pan/whatever to heat up. Whatever power source is coming in has to be converted to a high frequency AC signal.

I'm not understanding how feeding the stove unit with DC rather than AC would provide any kind of added efficiency. Whatever power is coming in has to be converted to a high frequency AC signal at the burner. Why would feeding the stove DC power create some kind of efficiency?

dj
 
Feb 16, 2021
544
Hunter Legend 35.5 Bellingham
OK, so I'm not, obviously, well enough versed in the actual units - but I don't understand this question. Induction heating is, by definition, done with AC power. The unit on the stove top must be using AC to heat the cooking pot/pan/whatever.

Induction heating accomplishes it's heating capabilities via a rapidly oscillating magnetic field what causes the ferro-magnetic material of your pot/pan/whatever to heat up. Whatever power source is coming in has to be converted to a high frequency AC signal.

I'm not understanding how feeding the stove unit with DC rather than AC would provide any kind of added efficiency. Whatever power is coming in has to be converted to a high frequency AC signal at the burner. Why would feeding the stove DC power create some kind of efficiency?

dj
‍Idunno
Gemini says it goes from AC to DC and then back to high frequency AC again. I assumed everything on the boat is DC and it’s more efficient to not invert just to convert.
I have no idea.

“An induction stove uses both AC and DC. It plugs into standard household AC mains, which is then internally converted to DC and finally transformed into a high-frequency AC to generate the magnetic fields needed to heat your cookware.”
 
May 17, 2004
6,156
Beneteau Oceanis 37 Havre de Grace
‍Idunno
Gemini says it goes from AC to DC and then back to high frequency AC again. I assumed everything on the boat is DC and it’s more efficient to not invert just to convert.
I have no idea.

“An induction stove uses both AC and DC. It plugs into standard household AC mains, which is then internally converted to DC and finally transformed into a high-frequency AC to generate the magnetic fields needed to heat your cookware.”
Once again AI shows it's not all that smart. All the induction stoves I"ve seen for marine use (both of them) are AC.
I think Gemini got it right though. The cooktop is alternating current, but at a very high frequency. An AC cooktop first rectifies the incoming AC to DC, and then converts that to a higher frequency alternating current for the induction. Wikipedia says the induction is done at 25-50 kHz, and this site gives a little more detail - https://mecs.org.uk/blog/induction-stoves-not-inductive-loads/.

Assuming that’s true a DC unit could save some efficiency in that first step, but only if the electronics use about 12V natively. Otherwise they’ll still need to convert the incoming DC to some other voltage anyway.
 

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
Aside from frequency, there is also the voltage side of the equation.
Another from GeminAI:

1. The Voltage Inside the Stove
While your stove plugs into a standard 120V or 240V home outlet, the internal electronics transform that power. To create the high-frequency alternating current needed, the internal inverter pumps anywhere from 200V to 600V through the copper coils beneath the glass. This higher voltage is necessary to force a massive amount of electrical current through the coil at incredibly high speeds (the 20–50 kHz frequency).
 
Feb 16, 2021
544
Hunter Legend 35.5 Bellingham
Practically speaking, it seems just going with an AC cooktop is the way to go. I have a Duxtop one that shows it uses 1800W. My West Marine inverter puts out a modified sine wave at 1500VA (4000VA surge max 15 seconds). Not sure how to convert the two, but the cooktop does not heat when powered by the inverter, so I assume output of the inverter is insufficient. Is there a cooktop that would work with my inverter? Any recommendations?
 

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
Interesting.
I have also have a Duxtop. It says model: BT-M20B / 9100MC/ 9120MC
It is also 1800watts - we might have the same.
For casual conversation, watts and vac can be considered the same thing.

This convo actually made me take it out today for a big pot of spaghetti sauce for dinner and freeze leftovers.

Anyway - no problems using the Magnum 2812 inverter with mine.
I just did a quick check on starting it up and it seems to pull ~70A off the battery at startup, about 1/2 power.

I wonder if the output on your inverter is dirtier and the electronics on the Duxtop don't like it somehow?
I presume your Duxtop works off shore power or at home.

EDIT: A couple more tests...
It starts up at level 5.0 (320F), draws ~70A off the battery.
Cranking up to max, 10.0, it draws ~145A off the battery.
 
Last edited:

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
Back on the topic of pulse heat moderation - GeminiAI reports the below about my Duxtop.
It generally matches the behavior I have noticed.
It clicks on/off regularly at low settings - like when simmering spaghetti sauce for a couple hours.

Duxtop model: BT-M20B / 9100MC/ 9120MC ; GeminiAI:
  • Low Settings (Settings ~1.0 to 3.0 or 4.0, depending on the model): They pulse. For example, if you set it to a low level meant to average out to 200W, the machine will actually blast around 400W–500W of power for a few seconds, then drop down to 0W for a few seconds to average it out. You will typically see this visually if you are simmering something delicate—it will boil furiously for a moment, stop completely, and then boil again.
  • Medium to High Settings (Settings 3.5/5.0 and up): They switch to continuous power. The induction coil stays on 100% of the time, feeding a steady stream of consistent energy into your pan.
 

dLj

.
Mar 23, 2017
5,095
Belliure 41 Back in the Chesapeake
I think Gemini got it right though. The cooktop is alternating current, but at a very high frequency. An AC cooktop first rectifies the incoming AC to DC, and then converts that to a higher frequency alternating current for the induction. Wikipedia says the induction is done at 25-50 kHz, and this site gives a little more detail - https://mecs.org.uk/blog/induction-stoves-not-inductive-loads/.

Assuming that’s true a DC unit could save some efficiency in that first step, but only if the electronics use about 12V natively. Otherwise they’ll still need to convert the incoming DC to some other voltage anyway.
That's interesting.

So potentially there could be minor efficiency but as you say, only if the unit wants 12V DC. I'd also wonder about the line loss bringing DC over to the stove, well, if it's fair distance from the batteries otherwise it wouldn't matter.

I've only worked in industrial induction systems. They didn't have an internal conversion to DC - at least not to my knowledge.

I do have an induction stove in my kitchen at my house. Which I find I don't actually like but I cook (well now only on my boat) a lot of non-traditional dishes that can't be done on induction...

dj
 
Feb 16, 2021
544
Hunter Legend 35.5 Bellingham
Inte
Interesting.
I have also have a Duxtop. It say model: BT-M20B / 9100MC/ 9120MC
It is also 1800watts - we might have the same.
For casual conversation, watts and vac can be considered the same thing.

This convo actually made me take it out today for a big pot of spaghetti sauce for dinner and freeze leftovers.

Anyway - no problems using the Magnum 2812 inverter with mine.
I just did a quick check on starting it up and it seems to pull ~70A off the battery at startup, about 1/2 power.

I wonder if the output on your inverter is dirtier and the electronics on the Duxtop don't like it somehow?
I presume your Duxtop works off shore power or at home.

EDIT: A couple more tests...
It starts up at level 5.0 (320F), draws ~70A off the battery.
Cranking up to max, 10.0, it draws ~145A off the battery.
Interesting. What inverter do you have?
I am able to use my 700w Emerson microwave for about 1 minute before it trips the 100A main house breaker at the battery combiner. Draw on the battery is 92A until it trips. Not sure if there’s an issue with my inverter or if this is behavior I should expect.
 
Last edited:

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
My inverter is a Magnum 2812. 2800w continuous.

You should not show that much (92A) at the battery when drawing 700 watts.
Amps x Volts = Watts.
700w/92a => 7.6 volts, and obviously your battery is not getting pulled down that low.

You may very well have undersized cabling or connections that are not up to torque or have some corrosion going on.
It is probably a good thing the breaker flips.

More example/math from GeminiAI
A Quick Example
Imagine you are running a 1,200-watt appliance on a 12-volt system.
  • With Proper Wiring (No Voltage Drop): The inverter receives a full 12V.
    $$\frac{1200\text{W}}{12\text{V}} = 100\text{ Amps}$$
  • With Undersized Wiring (Severe Voltage Drop): The thin wires choke the voltage down to 10V by the time it hits the inverter.
    $$\frac{1200\text{W}}{10\text{V}} = 120\text{ Amps}$$
Your battery monitor will show that extra 20 amps being drawn.

The Hidden Danger: Heat
That extra energy doesn't just disappear. The combination of high current and high resistance turns the undersized wires into heating elements. If your wires are getting warm or hot to the touch when running a load, they are dangerously undersized and present a serious fire hazard.
 
  • Like
Likes: kloudie1
Jun 17, 2022
539
Hunter 380 Comox BC
Practically speaking, it seems just going with an AC cooktop is the way to go. I have a Duxtop one that shows it uses 1800W. My West Marine inverter puts out a modified sine wave at 1500VA (4000VA surge max 15 seconds). Not sure how to convert the two, but the cooktop does not heat when powered by the inverter, so I assume output of the inverter is insufficient. Is there a cooktop that would work with my inverter? Any recommendations?
I'd get a 2400W pure sine wave inverter, like the victron 3000/120 (3000VA). You will have to upgrade your electrical system to match (cables, fuses, possibly battery bank size). Voltage drop is the enemy here.

Anytime you power sensitive electronics, a pure sine wave is preferred. Even the modified sine wave inverters can have a pretty rough ac output compared to shore power or a generator. You need an inverter that can react quickly to the switching on off of the cooktop to maintain a steady voltage, so oversizing helps in this respect. The 1800W cooktop could draw up to 1900-2100VA (volts-amperes) continuously due to the nature of the internal electronics.

When it comes to sizing inverters, it's the loads VA that matters, not the watts. Watts only apply to simple resistive loads, like a water heater.

A 1000W microwave will draw around 1600VA (power factor of microwaves is around 0.5 to 0.75)
The power factor of a quality induction cooktop should be 0.95 or higher (assuming they have power factor correction circuitry).


Recommended setup:

Mid grade hobb like duxton or changbert
Victron 3000/120 inverter
4/0 or (smaller if paired) conductors from the battery to the inverter (note the abyc requirements for fusing parallel conductors)
Class t fuses
300Ah or larger lifepo4 bank, recommend around 600Ah. Check the continuous rating of the cells and the bms.
Charging system that can keep up (alternator, solar, etc...)
Low loss connections /Crimps everywhere (see Will Prose video on youtube)

Yes, a simple change can snowball quickly.

Why lifepo4? Because they maintain a much higher voltage under load compared to lead batteries (they have lower internal resistance). You'll typically see around 13.1 to 13.3 volts under 100A with lifepo4, whereas you'd see 11 to 11.5V under same load with a lead acid battery bank, and much more internal heat build up in the lead batteries, reducing efficiency.

Going to induction for an off grid boat is something I would do only after modernizing the rest of the electrical system, it should be the last step. Building a boat to use only electric heating is not cheap, it's much cheaper to keep using gas UNLESs you are crusing the world and don't want to deal with all the different types of connections or you are in a very hot climate and don't want to heat the boat as much when you cook or put a lot of moisture in the boat 9very cold climate).

You're looking at at least $8000-$10 000 including batteries, wiring, fuses, bus bars, solar, alternator, regulator, etc... and about 2 weeks of work, if you know what you're doing. Plus electricians time.

In the pacific NW, 400-600Ah of lithium and 600 watts of solar will serve most under 40 ft boats well and be self sufficient for power off the grid from late April to early September. On really good days, you can even heat hot water tank as a dump load instead of waisting solar after the batteries are full. This would work for short simple meals on induction (coffee, eggs, soup) anything you can cook under 5 to 10 mins. Longer than that and you'd need more batteries and solar or keep the propane stove for the more intricate cheffy meals.

The other important consideration when sizing the dc system is the efficiency and daily draw of your refrigeration sytem. Some under 40ft boats draw 60Ah, other 150Ah a day just to make ice and keep the beer cold. We know we draw 4.5 A on a 15/14 min duty cycle in the summer, A bit more if the starboard side is in full sun in the afternoon (up to 15 min on, 8 min off).... there's more insulation to be done between the hull and ice box. 60Ah for beer, a pot of coffee on induction (kettle) costs about 6-7 Ah. Heating the hot water tank costs about 70-85Ah.


Here's a good test... can you run a hair dryer off the inverter on high setting for 12-15 minutes with nothing tripping , nothing getting hot (crimps, bus bars, fuses, battery switches, battery itself) and battery voltage staying above 11.5v? If the answer is no, then your electrical setup needs work before considering off grid induction stove use.
 
Last edited:

MFD

.
Jun 23, 2016
287
Hunter 41DS Pacific NW USA
I got curious about the VA vs. watts rating thing again.
I know they are different, and this is once more if from GeminiAI so talk with a grain of salt, but I didn't realize that a rule of thumb was to presume an 80% difference.

From GeminiAI:

Manufacturers often use VA because it is the most technically accurate way to measure what an inverter can handle, but a 1,000 VA inverter is not the same as a 1,000-watt inverter.
The Crucial Difference: Real vs. Apparent Power
  • Watts ($W$): This is Real Power. It is the exact amount of electricity an appliance consumes to do actual work (like heating a element or lighting a bulb).
  • VA (Volt-Amps): This is Apparent Power. It is the total amount of electricity the inverter has to send down the wire.
The classic electrical analogy is a mug of root beer:
  • The liquid root beer is the Watts (the actual, useful stuff you want).
  • The foam on top is Reactive Power (it doesn't do any work, but it still takes up space in the glass).
  • The entire mug (liquid + foam) is the VA. The inverter has to be big enough to hold the whole glass, even the foam.
How to Convert VA to Watts
To find out how many real watts your inverter can run, you have to multiply the VA rating by the Power Factor (PF) of your appliances. The power factor is a decimal between 0 and 1.
$$\text{Watts} = \text{VA} \times \text{Power Factor}$$
If you don't know your appliances' power factors, the industry standard is to assume a 0.8 Power Factor as a safe rule of thumb.
The Math: If you have a 3,000 VA inverter:
$$3,000\text{ VA} \times 0.8 = \mathbf{2,400\text{ Watts}}$$
So, your 3,000 VA inverter can safely run about 2,400 Watts of real-world appliances.



I also knew VAwas an AC power thing only, but thought I would ask.

is VA rating appliable only to ac or also dc?

The VA (Volt-Amps) rating is applicable only to AC power. You will never see a DC system rated in VA; DC systems are always rated strictly in Watts.
Here is why:
In DC Power: There is no "Foam"
Remember the root beer analogy where Watts is the liquid and VA is the whole mug (liquid + foam)?
In a DC (Direct Current) system, electricity flows continuously in one direction. Because there is no alternating cycle, inductive loads (like motors) cannot cause the voltage and current to get out of step with each other.
This means in DC, there is zero foam. Every bit of electrical pressure (Volts) times the volume (Amps) goes directly into doing real work (Watts).
The math for DC is always perfectly clean:
Volts (DC)×Amps (DC)=Watts
Summary of the Rules
  • AC Power: Uses Watts (real power) and VA (apparent power) because the "foam" (reactive power) forces engineers to measure them separately.
  • DC Power: Uses Watts for everything. Volts times Amps is Watts, so there is no need for a separate VA rating.
If you are looking at the DC input side of your inverter (the battery side), any power specs listed will be in Watts or Amps, never VA.
 
Jun 17, 2022
539
Hunter 380 Comox BC
Inverters spec output rating and efficiency, never dc input rating. They may spec dc charging current though for inverter/charge. VA is what we need to pay attention to when sizing ac equipment for an inverter.

Residential power is billed in watts because we don't use many large reactive loads at home (overall). Large industrial plants with many electric motors are billed in VA as the utility needs to account for the actual load on the grid . This is why we are not accustomed to VA.

This is also why many boaters get frustrated after spending loads of money on equipment that doesn't work... it wasn't spec ed correctly or the system as a whole was not considered.

Take a microwave .... they are sold and advertised based on their cooking power (say 1000W), but the spec plate will likely specify power input , say 1400 Watts, voltage 120V and may specific current 13 Amps. The magnetron has roughly a 40 pct loss.
 
Last edited: