Jackdaw;
Prior to being a marine dealer, I was an accident reconstruction investigator for insurance companies who worked with fire marshals. They all said when the total sum of the breakers exceeds the main breaker, not only is it against code but anything can happen. I recall two incidents where the total sum exceeded the main breaker and people died involving boats. So when I look at something, I look at the situation from a safety advantage too and nothing others say will ever deter me from that line of thinking involving safety paticuraly around water.
Dave pretty much every boat on the water above 30' has an AC panel where the breaker sums exceed the capacity of the main breaker. There is nothing in the ABYC standards that limits branch breakers from exceeding the main breaker capacity. This is why you have a main breaker... Below is a very popular bone stock factory configuration for many boats over 30', including factory boats from Catalina and Hunter..
30A Main Breaker = 10GA wire
Battery Charger = 15A Breaker / 14GA wire
Water Heater = 15A Breaker / 14GA wire
Port Outlets = 15A Breaker / 14GA wire
Starboard Outlets = 15A Breaker / 14GA wire
Sometimes a Microwave breaker is also thrown in...
On the land side this is also not a requirement under the NEC Standards..
[FONT=Arial, Helvetica, sans-serif]Q8. Is there a code limitation as to the total ampere rating of all circuit breakers in a panel? Example: Could the total ampere rating of all circuit breakers in a 100A panel exceed 100A?[/FONT] [FONT=Arial, Helvetica, sans-serif]
[/FONT]
[FONT=Arial, Helvetica, sans-serif]A8. This is not a Code issue. The sum of the ampere rating of the circuit breakers in a panelboard is irrelevant. As a matter of fact, it is very common for the total ampere rating of the branch breakers in a panelboard to far exceed the rating of the panelboard.
[/FONT][FONT=Arial, Helvetica, sans-serif]
All one has to do is examine this[/FONT]
[FONT=Arial, Helvetica, sans-serif] Square D 60 Circuit Main Panel Board[/FONT][FONT=Arial, Helvetica, sans-serif]
to realize there is no requirement on land for the branch breakers to not exceed the panel main breaker.
When you consider there is room for 60 circuits/breakers, and the smallest land breaker is 15A, you will quickly realize that just fourteen 15A breakers exceeds the 200A main breaker..... We have over 30 breakers in our 200A panel with the smallest breaker being 15A......
I can nearly guarantee that everyone's home AC panel has breakers that exceed the main panel breaker rating. I can't recall the last time I saw a home distribution panel where the sum of the breakers did not exceed the main breaker...
[/FONT]