Where to Look Next

Status
Not open for further replies.
J

John Crossen

I have a 12-year old refer sys; its a single compressor unit that feeds a 1/4" "T", with each leg going through a solonoid valve and then to a cold plate in the refer or freezer box. I have significant corrosion on most all parts of the compressor, but no apparent leaks. My compressor starts and runs OK, but the sight glass goes from nearly full to approx 1/4 full, the hermetically-sealed compressor gets so hot you can't touch it, and the boxes both cool to about 40 degrees F; the compressor runs until it overheats and shuts off (12-18 hours later). The cooling water flow remains constant, and warm (not hot). I've had the system checked for leaks (none found) and the DX valves adjusted--all without change in the performance. I don't know where to look next-any suggestions/help would be most apprteciated.
 
G

Gary Buttrey

Is it?

John, is it a CombiCold system? If so, how many amps is it drawing?
 
R

Russell Sager

Operating Pressures?

Hello, Is it possible to get the operating pressures of the system? Both discharge and suction pressure. Also type of refrigerant. Thanks
 
J

Jim Hague

Refrigerant

Your observations of the sight glass suggest that the unit is low on refrigerant. Remember - Homogeneous materials aren't and Hermetic systems ain't either.
 