Good day all,
On an O'Day Mariner, originally with no electrical system, I built a stern rail and installed a 95 watt solar panel.
I'm using all LED lighting and other than a Garmin , VHF, a fan and some other tidbits my usage is about 80 - 120 watts per day depending on what I use and for how long.
The set-up is as follows;
I ran 10ga. wire from the panel to a Genasun MPPT Charge Controller, a distance of about 15'.
The controller is next to the battery, a 12v. 100Ah deep cell with 10g.wire from the Controller to the Battery.
From the Battery, a 10ga wire to a "Blue Sea Weather Deck switch panel" with idividual fuses for each circut.
What I don't have fused and what concerns me is the 10g, line from the Battery to the Switch Panel, a distance of about 6'.
What I was thinking of using was a "Blue Sea Systems 5191 Fuse Block Terminal", [30-300 amp] that attaches directly to the battery post, but the lowest amp fuse is a 30amp.
As all the circuits are individually fused, I'm really looking to protect the wire from the battery to the panel against shorting.
Does this sound reasonable?
Thanks,
Rob Jones
On an O'Day Mariner, originally with no electrical system, I built a stern rail and installed a 95 watt solar panel.
I'm using all LED lighting and other than a Garmin , VHF, a fan and some other tidbits my usage is about 80 - 120 watts per day depending on what I use and for how long.
The set-up is as follows;
I ran 10ga. wire from the panel to a Genasun MPPT Charge Controller, a distance of about 15'.
The controller is next to the battery, a 12v. 100Ah deep cell with 10g.wire from the Controller to the Battery.
From the Battery, a 10ga wire to a "Blue Sea Weather Deck switch panel" with idividual fuses for each circut.
What I don't have fused and what concerns me is the 10g, line from the Battery to the Switch Panel, a distance of about 6'.
What I was thinking of using was a "Blue Sea Systems 5191 Fuse Block Terminal", [30-300 amp] that attaches directly to the battery post, but the lowest amp fuse is a 30amp.
As all the circuits are individually fused, I'm really looking to protect the wire from the battery to the panel against shorting.
Does this sound reasonable?