For the past few years I have had an intermittant problem with the ground alarm on my ProMonitor Unit that is getting worse.When I connect the Shore Power Cable Main 1, I often get the ground and galvanic isolator alarm on the ProMonitor unit. Sometimes I can reset the alarm but more recently I can not reset the alarm. Sometimes just the ground alarm clears but the galvanic isolator alarm remains in.The alarm comes in even though the main #1 AC distribution breaker is off, i.e. no loads on the bus. I do not have the problem when I connect the second shore power cable for the Air Conditioning unit. Both lights for cable #2 remain green "Normal" even when the Air Conditioning starts. I have switched the two cables but the alarm remains on line #1 indicating that the problem is on the boat.When I can reset the alarm, the circuit runs fine unless I start a large load like the water heater. When I switch on the water heater both green lights for line #1 on the Pro Monitor system get very dim and after a few minutes both change to alarm.Do I have a ground problem on line # 1 or can the Pro Monitor be faulty. How can I tell?Thanks in Advance