The refrigeration lines from my compressor to unit is sweating a lot. The water drops down off them and runs down and under the hot water heater. It builds up under the seatee. Is this common on hunter 340 sailboats. I am not sure how to correct this. Thanks for any help
 
Oct 29, 2005
2,355
Hunter Marine 326 303 Singapore
I don't think its normal. My refrigeration lines doesn't sweat. No idea what could cause this.

Ken Y
 
Jan 7, 2011
4,723
Oday 322 East Chicago, IN
Whoever installed my refrigeration put pipe insulation on the pipes…

I don’t get much (if any) sweat.


Greg
 
  • Helpful
Likes: JamesG161
Jun 15, 2012
694
BAVARIA C57 Greenport, NY
Sweating is normal on the low or suction side of any refrigeration or a/c lines in a hot, humid environment. The cure is pipe insulation.
 
  • Like
Likes: JamesG161
May 24, 2004
7,129
CC 30 South Florida
Like others have pointed out pipe insulation is the answer. Just make sure is attached firmly to the AC line to minimize hot and humid air from getting in between the insulation and the line. The biggest headache is catching and draining that condensation before it creates a puddle.
 
Apr 3, 2015
7
Hunter 27 Chicago
You need to check with the manufacturer of the refrigeration unit in question. On many refrigeration (not air conditioning) systems the hot high pressure liquid line going to the evaporator is mechanically attached to the cool suction line which travels back to the compressor in what is called a desuperheater. This allows the suction line to cool down the liquid and eliminate vapor bubbles in this liquid. This also warms up the suction line and helps eliminate excess sweating. It is still necessary to insulate the lines thoroughly, sealing ends and openings. Hope this helps.
 