Power Down

Status
Not open for further replies.

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
Went to the lake yesterday and found no power on our 272 LE...the 110 volt system appears to have shut down completely...no juice...I first checked the
GFCI and looks tripped, but will not re-set.....the entire system worked fine
last Sunday....Air Conditioning, etc...came right on....now nothing...checked the dock connections and can not tell if the 4 circuits at each pedestal are working.
I have one bad battery below and wondered if is possible the charger shut it down trying to keep it charged.....Have two new batteries but have not installed as the boat has been starting just fine.....

Why will the reset button on the galley GFCI not work ?....it controls both 110
circuits plug ins, i.e. galley and head....but can only be reset at the galley..
Should I try shutting off the charger and then try resetting the GFCI?..
thanks for any help, Pat
 
Nov 8, 2010
11,386
Beneteau First 36.7 & 260 Minneapolis MN & Bayfield WI
Do you not have an AC panel with a breaker and a pilot light?? That would tell you if you are getting AC onto the boat.

Do you have more than one GFI on the circuit? If yes they can be hard to reset when tripped.

I would be very careful and maybe get professional help. AC and water is a very dangerous combination.
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
thank you for answering...yes, have AC panel with breakers. two switches, one for outlets and one for Mermaid AC & Statpower 10 charger....plus polarity light....nothing is now on... everything worked fine Sunday....the GFI controls the main AC panel and two duplex outlets; one at the galley, and also the duplex outlet in the head medicine cabinet...The shore power cord is 26 years old, but as I say, worked fine Sunday...they were working on the dock power pedestals over the weekend, but it has worked fine since then until yesterday...there has been no rain...thanks, Pat
 
Jun 2, 2011
347
Hunter H33 Port Credit Harbour, ON.
If there is no power at the GFCI the reset will not engage. Sounds like you have no AC coming into the boat.
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
I appreciate the information. I'm not convinced either that the power is even getting to the boat....at our 4-boat pedestals there are 4 sets of outlets, each with resets and there is also a large lid that you can lift and throw the power to each slip....it looks like there is a little lighted window at each of the numbered resets, but only one has a blue light in it ...the others are just white....why would one be blue and the other 3 clear or white? The Erickson 32 next to me seems to be the only one lit....oh, if I could only try his power cord.....that appears to be on.....If I disconnect my cord & hit the reset
on the pedestal, if the issue is the cord, then wouldn't the reset stay in and power come back to by portion of the pedestal? thiis probably makes no sense....pat
 
Feb 26, 2004
23,067
Catalina 34 224 Maple Bay, BC, Canada
It's Thursday

Pat, it sounds like you have no power to your boat.

Since it's still a weekday, have you considered going to the harbormaster and telling him the wiring they did on the dock may not be either finished or correct?

Good luck.
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
Re: It's Thursday

Well, the boat had power....110 for the Mermaid AC....but the two duplex outlets are
still not working....had a guy look at it...put in a new duplex outlet w/new gfi and neither out let is working as long as the GFI is part of the ciircuit...the circuit works fine w/o the
GFI added...by the way...the Air Conditioner is on it's own circuit controlled by a switch.
The guy thinks the new GFI is faulty...but the issue I think is he doesn't know how to
do the installation with the two duples outlets operating off of one GFI...any thoughts?
I am going to have a real licensed electrician look at it next week....Pat
 

Apex

.
Jun 19, 2013
1,212
C&C 30 Elk Rapids
if the gfci is not "operating" then there is a ground fault, and it IS actually protecting you. You will need to find the source of grounding.

A recent personal example: our sewer lifting pump was tripping the GFCI. The pump seemed to operate properly for a veryshort time, but would trip continuously. It would operate ok on a non-gfci circuit though. I replaced the pump thinking worn bearings were creating overload, but turns out the float switch was cracked, and the switch inside was grounding through the water.
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
thank you for the confirmation of what I believe....somewhere there is an issue....We did find corrosion on the shore power cord (27 years old), but it is working normal....I have been having an issue with the automatic float switch or the auto part of the manual/auto
rule wall switch....auto is no longer working...but I doubt that is the issue.
 
Jan 22, 2008
880
Fed up w/ personal attacks I'm done with SBO
There's a little more to it

It is true the GFCI protects against ground faults but it must be installed correctly to even function. When you say you had "some guy" look at it, there's a red flag. He may be qualified, I can't possibly know but then again . . . .

The installer must know the difference between 'Line' and 'Load' wires and that includes the white neutral wires. They must be connected to the proper terminals on the GFCI. If a receptacle type GFCI is used, that's 4 wires in 4 correct places not counting the ground.

There's a difference also between 'tripping' and 'not operating.' Operation requires a functioning GFCI, proper installation and power applied. If any of those three are incorrect your system will not work. Note also that the GFCI protects only itself and the circuit downstream.

Finally, and I apologize for even mentioning something so basic, a new GFCI comes out of the box in a default tripped condition. After installation and application of power it must be reset to function.
 
Last edited:
Jan 24, 2005
4,881
Oday 222 Dighton, Ma.
Pat,

The problem could be at their load center. If they used Aluminum conductors in their meter sockets and load centers, the problem could be corrosion at the meter lugs or the load center lugs. Generally what happens is after a period of time Aluminum will loosen in the lugs. If there's a heavy load on the system such as air conditioning, the lugs will build up a lot of resistance and get pretty hot and the connection is lost.

A lot of times if the wires aren't too burnt, the electrician can get away with de-energizing the load center or meter socket and remove the conductors, wire brush them, and add an inhibiter grease to them and tighten them back on the lugs.
As a lineman for the power company I worked for, I had many of these from time to time. Aluminum can be a problem sometimes. You can tighten the lugs on Aluminum conductors and come back in two weeks and get a few more cranks on them. I would talk to them about checking their side first and then take it from there.
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
Trinkka, are you speaking of the dock side power pedestals (load center)? the dockside
power is working as the AC on the boat is working....we did find a bit of corrosion on the
27 yr. old shore power cord, but we removed the corrosion and the AC is working so we
have power getting to the boat....I truthfully don't think the fellow that was nice enough to come to our boat dwelt with the two duples outlet ganged together correctly....but
the elec. eng. that has the Erickson 32 next to me is returning from vacation today..&
Heather called him and he'll get to it before the weekend. All your thoughts and suggestions are appreciated. Patrick
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
About all we ever plug is is some Vornado fans, to augument the AC. I'm running by the boat today to put up some poster's for our Labor Day Weekend Show....need to have a boat to play on. I can sail at least...what 110 volt outlet using things can you think of...
charger? fans, would a seperate stereo amp use power, vs. the battery operated clarion stereo/cd player? I'm at a loss....how about bilge pump...I think that is off batteries. thanks for your help. Pat
 
Jan 24, 2005
4,881
Oday 222 Dighton, Ma.
Trinkka, are you speaking of the dock side power pedestals (load center)? the dockside
power is working as the AC on the boat is working....we did find a bit of corrosion on the
27 yr. old shore power cord, but we removed the corrosion and the AC is working so we
have power getting to the boat....I truthfully don't think the fellow that was nice enough to come to our boat dwelt with the two duples outlet ganged together correctly....but
the elec. eng. that has the Erickson 32 next to me is returning from vacation today..&
Heather called him and he'll get to it before the weekend. All your thoughts and suggestions are appreciated. Patrick
Yes Pat.
The shore power. Corrosion is always a sign of problems. Also, when electrical connections with a heavy load get loose or corroded so bad that the power goes off and on, the device usually gets real hot. I used to put my finger on the breaker and if it was bad it would be hot with a heavy load on it. Good luck with that. Electricity is funny stuff.

Joe
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
Trinkka, the bit of corrosion we took off was at the load center end of our shore power cord....(27 years old)..then.....what items on a boat like ours would require an outlet....I guess TV, battery charger, fans, etc. can't thnk of much else, & I'm not totally sure of the battery charger...I talked to the elec. guy that has been trying to help me and he says he thinks he's got it figured out.....we shall see tomorrow....I take it bilge pump uses battery...bilge switch is battery, stereo is battery, coffee is a gift of God...lights are battery, depth sounder, gps is garmin handheld on pedestal, ????anymore? Pat
 
Jan 24, 2005
4,881
Oday 222 Dighton, Ma.
I think that you need to use the process of elimination Pat. If the GFI won't reset, there's a fault in the circuit and it's probably your battery charger. Disconnect it and see if the GFI resets. You really don't have much electrical load on that boat so it has to be a fault. If one of your batteries is bad, you need to remove it.
If that don't work, try unplugging electric gear or turning off individual breakers until you can get the GFI to reset. It may be time for a new shore power cord. At any rate, try using the process of elimination and see what you can find.
Good Luck!
Joe
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
you are probably right and the process of elimination has led to the battery charger...At this moment, I only know where the charger is, not how it was wired by the electrician who installed it. there is no other constant than a charger trying to charge a battery charger.
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
Trinkka, I said that wrong....charger trying to charge a bad battery....I have two new one's under the helmsman seat. Pat
 

Pat

.
Jun 7, 2004
1,250
Oday 272LE Ninnescah Yacht Club, Wichita, Ks.
We replaced the duplex outlet w/GFIC this morning....I feel much better...also replaced both batteries with new....the charger seemed happier and so am I. Thanks to everyone who tried to help me....Patrick in Wichita
 
Status
Not open for further replies.