Overloaded our electric system.

Les356

.
Jul 16, 2017
11
Hunter 33 Eau Gallie, Florida
We overloaded our electric system while on shore power. Used a/c in hot weather and then turned on hot water heater.
Main breaker popped, now outlets do not work and inverter is only showing 12.5 volts. I replaced the gfci, but still no juice to outlets.
seven days from home, now in beautiful Marathon, can’t find where the neutral wire from the gfi goes. Got juice to the gfi, but doesn’t
seem to function. Any ideas?
 
Dec 2, 2003
766
Hunter 260 winnipeg, Manitoba
If you have power to gfci but can’t get it to reset there are a few possibilities - hot and neutral on conductor from main panel to gfci reversed? Conductors from main panel connected to load side of gfci rather than line side.

Are there any led’s on the gfi and are they illuminated?

Neutral wire from gfci should go to the main neutral bar where the main breaker is located.

The above is assuming this is the wiring onboard your boat and that the gfci is downstream from your main breaker.
 
  • Helpful
Likes: ggrizzard

jviss

.
Feb 5, 2004
7,090
Tartan 3800 20 Westport, MA
For some circuit breakers, you have to push the lever all the way to the OFF side before it will turn back on.
 
Feb 6, 1998
11,772
Canadian Sailcraft 36T Casco Bay, ME
If you have AC there should have been a second 30A service installed. Your 30A service should not exceed 24Aand this is with 100% perfect , new & clean connections.. Try locating a second 30A breaker in the inlet path. if the distance between inlet and panel is more than 10 wire feet a second breaker is required..
 
  • Helpful
Likes: ggrizzard
Oct 26, 2010
2,234
Hunter 40.5 Beaufort, SC
Don't know the age of your Hunter, but on some (at least in the 90's) there are two small pop-out breakers (push button) generally right below or very near where shore power connects to the boat. There is one on the black (hot) and one on the neutral (white) line. It is possible one of these has failed (most likely the neutral) if you have 120V to the gfci (juice as you call it). I had one of these fail on mine.
 

Les356

.
Jul 16, 2017
11
Hunter 33 Eau Gallie, Florida
Don't know the age of your Hunter, but on some (at least in the 90's) there are two small pop-out breakers (push button) generally right below or very near where shore power connects to the boat. There is one on the black (hot) and one on the neutral (white) line. It is possible one of these has failed (most likely the neutral) if you have 120V to the gfci (juice as you call it). I had one of these fail on mine.
Thank you. It’s a 2008 but no breakers.
 
Oct 26, 2010
2,234
Hunter 40.5 Beaufort, SC
Odd to not see some sort of circuit interupter near the shore power inlet on the boat. I thought it was an ABYC standard requiring some sort of circuit breaker withing a few inches of where shore power enters the boat.
 
  • Like
Likes: jssailem
Oct 26, 2010
2,234
Hunter 40.5 Beaufort, SC
Breaker within 10 ft of where shore power enters.
Thanks for the clarification. I have these 2 Pop-out breakers (30 amp each) right by my shore power inlet connection plus the regular AC breakers on the electrical panel. Just thought the breakers close to the input were "standard". I had one fail and had to replace one.
 
Dec 2, 2003
766
Hunter 260 winnipeg, Manitoba
You mentioned you had power to the gfci. That implies the problem is at, in or after the gfci. I confess I assumed everything after had been functioning and that there was no change. So, if the wiring at the unit is good (panel or inlet to line side of gfci) and you didn’t get a faulty, new unit (it happens) then the problem should lie after the gfci.

To test:
Turn off breaker
Disconnect load side wires from gfci. Turn breaker back on, Try to reset gfci. If it works you have confirmed an issue in the down stream wiring or any connected devices/loads. If it doesn’t recheck wiring from panel to line side of gfci. If wiring is all good you may have faulty gfci, try a new one.

Next steps if you were able to reset.
Turn off breaker
Unplug/disconnect any devices/loads from outlets or that are hardwired to the same circuit. (You mentioned charger/inverter showing 12.5v. Is it powered by ac from this same circuit? If so disconnect from the circuit as well)
On disconnected load side wires (downstream) at the gfci, with mult meter check for any voltage, assuming none switch to test continuity. Test for continuity between hot and neutral, hot and ground, finally check ground to neutral.
If there is any continuity you either have a hard wired load somewhere or a short.
If no continuity then reattach load side wires to gfci and see if it trips or if already tripped can it be reset?
If it can be reset then the problem lies in one of the loads/devices unplugged

If you have continuity in tests above, you have either a short, a load still attached to the circuit or both.
Steps from here would involve going from each outlet/box on the circuit to the next outlet/box and disconnecting the wires and testing for continuity in the upstream wires, then the downstream wires until you can localize the short/load.

Also just for further clarification as there appears to be some confusion based on the answers that have been provided. Is the gfci after the boats main ac panel or between the shore power connection and the panel?
 

Les356

.
Jul 16, 2017
11
Hunter 33 Eau Gallie, Florida
Odd to not see some sort of circuit interupter near the shore power inlet on the boat. I thought it was an ABYC standard requiring some sort of circuit breaker withing a few inches of where shore power enters the boat.
It’s a 2008 Hunter. I couldn’t find any circuit breakers there, and the only gfci I could find was the first duplex outlet near the panel. I searched for another but no luck.
 

Les356

.
Jul 16, 2017
11
Hunter 33 Eau Gallie, Florida
You mentioned you had power to the gfci. That implies the problem is at, in or after the gfci. I confess I assumed everything after had been functioning and that there was no change. So, if the wiring at the unit is good (panel or inlet to line side of gfci) and you didn’t get a faulty, new unit (it happens) then the problem should lie after the gfci.

To test:
Turn off breaker
Disconnect load side wires from gfci. Turn breaker back on, Try to reset gfci. If it works you have confirmed an issue in the down stream wiring or any connected devices/loads. If it doesn’t recheck wiring from panel to line side of gfci. If wiring is all good you may have faulty gfci, try a new one.

Next steps if you were able to reset.
Turn off breaker
Unplug/disconnect any devices/loads from outlets or that are hardwired to the same circuit. (You mentioned charger/inverter showing 12.5v. Is it powered by ac from this same circuit? If so disconnect from the circuit as well)
On disconnected load side wires (downstream) at the gfci, with mult meter check for any voltage, assuming none switch to test continuity. Test for continuity between hot and neutral, hot and ground, finally check ground to neutral.
If there is any continuity you either have a hard wired load somewhere or a short.
If no continuity then reattach load side wires to gfci and see if it trips or if already tripped can it be reset?
If it can be reset then the problem lies in one of the loads/devices unplugged

If you have continuity in tests above, you have either a short, a load still attached to the circuit or both.
Steps from here would involve going from each outlet/box on the circuit to the next outlet/box and disconnecting the wires and testing for continuity in the upstream wires, then the downstream wires until you can localize the short/load.

Also just for further clarification as there appears to be some confusion based on the answers that have been provided. Is the gfci after the boats main ac panel or between the shore power connection and the panel?
It may be that the new gfci is faulty. I’ll get a new one tomorrow. I can’t get voltage between the hot and neutral wires now, but I will try between the hot and the ground. See how it goes. The main panel is powered by shore power then to the gfi. Funny thing is the lights on the outlet switch and the microwave do not function. Thanks for your help. Inverter doesn’t seem to be charging so I’m running the engine right now to keep the batteries charged up.
 
Oct 26, 2010
2,234
Hunter 40.5 Beaufort, SC
You may not have one but mine do not look like a traditional circuit breaker you have on your panels. They are simply very small "buttons (2)" that pop out when they trip. When the fault is cleared, you can reset them by pushing them in. You can see what they look like by going to amazon and typing in "30 amp push button circuit breaker". I'm not saying that your problem or even that you have them. I just know they were on my boat and wanted you to know what they looked like. Maybe they got rid of them in later models.
 

Les356

.
Jul 16, 2017
11
Hunter 33 Eau Gallie, Florida
Cou
Thanks for the clarification. I have these 2 Pop-out breakers (30 amp each) right by my shore power inlet connection plus the regular AC breakers on the electrical panel. Just thought the breakers close to the input were "standard". I had one fail and had to replace one.
I couldn’t locate any breakers near the shore power plugs.
 
Jan 7, 2014
464
Beneteau 45F5 51551 Port Jefferson
Do you have power going through a transfer switch on an inverter? My Xantrex has a reset button but you said you had juice at the GFCI. The other issue could be a short in the heater element. It may be grounding the GFCI. Did you try leaving the heater breaker off.
 

Les356

.
Jul 16, 2017
11
Hunter 33 Eau Gallie, Florida
Do you have power going through a transfer switch on an inverter? My Xantrex has a reset button but you said you had juice at the GFCI. The other issue could be a short in the heater element. It may be grounding the GFCI. Did you try leaving the heater breaker off.
We turned off the heater right away after the main breaker blew.
power from the outlet switch to the gfci seems intermittent. I disconnected the output on the gfi but it still won’t reset. I’ll go through the reset procedure with the Xantrax again today
Very carefully with the gfci out of the system and see how it goes. Thank you all for your help.