Just finished it this week. I used a Square D, 30amp. load center with 2- 120 volt breakers. One 20 amp and one 15 amp. The receptacle is a weather proof/ tamper proof 20amp GFI. The receptacle box is the weather proof plastic one and the conduit is the 1/2" sealtite flexable type with fittings for it and a 30amp Marinco plug outside in the cockpit. I used #8 stranded wire rated at 40amps from the Marinco plug to the load center and #12 stranded wire rated at 20amps from the load center to the gfi receptacle. I plan to install another receptacle to the V-birth later.