Galvanic Isolators
I generally agree that Galvanic Isolators are best designed and built by professionals.However, FWIW:ABYC standards specify that the isolator must be capable of carrying 135% of the rated shore power current, in the event of malfunction in the AC breaker/circuit protection.ie: 30A 120V Shore Power requires 41 Amp rating.ABYC also requires the Isolator to equipped with a Status Monitor that provides an audible or visual indication that a fault has occurred. ABYC also requires that the indication must be readily apparent to the vessel operator (often requiring a remote monitor panel).The Fail-Closed (to short cct.) design is essential, and required for any shore-based application under the National Electrical Code (NEC), according to the effective grounding path requirements of section 250. This retains safety grounding, in the event of a failure, avoiding a potential hazardous situation.However, ABYC does not explicitly require ship-based electrical systems to meet the effective grounding path wording of the NEC, and therefore galvanic isolators, that have not been designed and tested to this requirement, could Fail-Open, resulting in injury or death.The current ABYC Standard A-28 lists the testing sequence of a Galvanic Isolator which includes AC Conductivity test, Galvanic Current Blocking, (AC superimposed Galvanic Current Blocking - if Capacitor Equipped), Vibration Test, Shock Test, Temperature Test, Short Circuit Test (Interrupting Capacity = 3kA for 30A), Strain Relief Test, and Ignition Protection test (if applicable). The requirements in general state that isolators be tested by an independent laboratory to establish the isolators compliance with this standard and that isolators be provided with instructions covering installation requirements including a complete set of electrical instructions with diagrams. Anyone interested can email me a fax number, and I’ll fax a copy (12 pages).The National Fire Protection Association also diagrams, and issues standards in a properly constructed and installed galvanic isolator.Regards,Gord MayGord@BoatPro.zzn.com