LPG not flowing to stove

Status
Not open for further replies.
Apr 29, 2012
10
Beneteau 393 Gloucester
Have recently purchased a used 393. It was laid up for the winter and we are not able to get gas flowing to stove elements (tanks are full). Is this likely due to a malfunctioning solenoid at the tanks?
Tks
 
Oct 6, 2010
119
Beneteau Oceanus 321 Carters Pt.
LPG not flowing

solenoid is most probable cause we had the same problem with our B 321 barely enough gas to light stove
(with some one stationed at the solenoid have another person turn the power on for the valve there should be an audable and strong "click" when the valve opens.On ours there was a muted click(old valve) replaced valve and system operating as designed. there is also the possibility of an isolaying valve in the system
 

Rick I

.
Jan 6, 2007
414
CS36Merlin and Beneteau 393 - Toronto
Many Beneteaus built 03/04 came with defective solenoids that quit after a while. Beneteau replaced some of these. Actually they referred me to the manufacturer who promptly sent me a new one.
 
Jan 22, 2008
8,050
Beneteau 323 Annapolis MD
It may take 10 seconds for gas to reach the stove while you hold the stove control open. Should be able to hear gas coming out the burners.
 
Jun 25, 2012
19
Beneteau 456cs Southport
Check the pinhole under the gas jets, it supplies the gas to the gas head. It often becomes clogged with over zealous cleaning, or oxidization, in my case, not in the pinhole but the surrounds.
Ross Gard
 