(To recap: The refer didn't work when I bought the boat two years ago, and there's no way of knowing how long it sat before that. First round of troubleshooting yielded 5 blinks on the freshly-installed troubleshooting LED, without trying to start the compressor- indicating the control module needed replacement.)
So... New control module finally arrived yesterday, and I installed it on the unit today. Connected all the wiring, flipped the switch, and... Huzzah! It came to life! :dance:
...For about 20 seconds. :cussing: Now the LED is showing three blinks.
Figuring that the unit had been sitting idle for a while, maybe the pressures in the lines need to equalize and get the refrigerant moving before everything evens out... Flip the switch off, wait 2 minutes, flip it back on. Huzzah! It came back to life! :dance: Even better, the plate in the ice box is cooled from 78 degrees to about 58! :dance::dance:
... For about two minutes this time, before the three-LED warning came back again. :cussing:
What the heck. Wait two more minutes, and give it one more try...
...And it kept working for about 10 minutes. Two blinks this time (Fan overcurrent). During these 10 minutes, the bearings in the cooling fan had given up the ghost (They were a bit noisy through all this...); Add THAT to the list of items to replace... :bang:
SO, I disconnected the fan (The boat has air conditioning running and the locker was open, so I figured I could get by for a short while). Crank it up one more time, and it runs for about 30 seconds before the Three-Blink LED kicks in again.
According to all the literature I can find, this indicates a compressor that can't get up to operating speed. Possible causes include...
a. Too much friction within the compressor [Replace compressor!
]
b. A major pressure imbalance within the system, or
c. Some jackweed put too much refrigerant in the system trying to charge it.
So... Any recommendations on what to do next?
(Richard Kollman, are you still out there?)
--Jon
So... New control module finally arrived yesterday, and I installed it on the unit today. Connected all the wiring, flipped the switch, and... Huzzah! It came to life! :dance:
...For about 20 seconds. :cussing: Now the LED is showing three blinks.
Figuring that the unit had been sitting idle for a while, maybe the pressures in the lines need to equalize and get the refrigerant moving before everything evens out... Flip the switch off, wait 2 minutes, flip it back on. Huzzah! It came back to life! :dance: Even better, the plate in the ice box is cooled from 78 degrees to about 58! :dance::dance:
... For about two minutes this time, before the three-LED warning came back again. :cussing:
What the heck. Wait two more minutes, and give it one more try...
...And it kept working for about 10 minutes. Two blinks this time (Fan overcurrent). During these 10 minutes, the bearings in the cooling fan had given up the ghost (They were a bit noisy through all this...); Add THAT to the list of items to replace... :bang:
SO, I disconnected the fan (The boat has air conditioning running and the locker was open, so I figured I could get by for a short while). Crank it up one more time, and it runs for about 30 seconds before the Three-Blink LED kicks in again.
According to all the literature I can find, this indicates a compressor that can't get up to operating speed. Possible causes include...
a. Too much friction within the compressor [Replace compressor!
b. A major pressure imbalance within the system, or
c. Some jackweed put too much refrigerant in the system trying to charge it.
So... Any recommendations on what to do next?
(Richard Kollman, are you still out there?)
--Jon