In the case of shore power - AC (safety) green is not connected to AC white (ground) anywhere on the boat. Instead AC (safety) green is goes to earth separately (usually by way of the motor block/shaft/prop assembly) and then necessarily via seawater back to the shore power source.
When the boat is out of the water this alternate AC safety green path back to earth (via seawater) no longer exists.
So when on the hard - this alternate AC (safety) green to earth path needs to be re established via a conductor from propeller/shaft to a ground rod.
Charles
Charles,
The reason we create this secondary path for the green safety wire, in marine electrical standards, is because marina wiring is and has been historically horribly unreliable.
In water you still always have two potential paths, back through the shore power cord, or if that safety green drops, as it does, then you still have the water path. Two safety paths intended to create redundancy based on the historical unreliability of marina wiring. the water path is an emergency last ditch safety back up. The shore cord green wire is primary.
On land the electrical pedestals are not being torn out by Buffy & Skippy in the new Sea Ray ripping the dock pedestal out by forgetting to unplug... Yards are
usually wired by a licensed pro, not Darrell & Darrell the dock boys who mix up green & white or white & black after Buffy & Skippy tear out the pedestal....
The systems in boat yards can be sketchy but are usually MUCH more reliable than a marina.. You don't need to bond the prop shaft IF the yard has a well wired system, which legally they should, and it should include green safety ground... If the marina has only a two wire system, no safety ground, then grounding the boat can be wise..