Neutral bonding
When we plug into 30 amp or 15 amp shore power, there are no problems with any protective non GFI devices {breakers}. We have recently moved to a new slip in our Marina that has GFI breakers on the Shore Power and now everytime we plug the power cord in, it trips the GFI breaker. I have turned the DC main off and any breakers on that panel. I turned off all the breakers on the AC panel. When I turn the main AC breaker on, it trips the GFI in the shore power {with none of the AC breakers in the on position}. There is a Xantrex Freedom 20 Inverter/Charger on our Hunter 356. This problem has occurred on 4 different 15 amp plugs fed by the Marina shore power. What could be causing this?
Ok, it is likely that the neutral is bonded to ground on the output of the inverter, because this follows ABYC code.
But, the inverter disconnects the neutral to ground bond when shore is live. That is a function of the internal transfer switch.
Here is what a reverse polarity light does:
It connects a light between the neutral and ground legs, which typically runs about 10ma of current.
The gfi units are set to 5ma trip.
Now, without a bona-fide reverse polarity issue, you shouldn't have any current between N to G.
So, I suspect that you have an on board wiring issue, or, it is possible that the shore wiring going to the gfi is reversed.
A gfi won't trip from reverse polarity, as long as there is no ground leaf age.
The shore neutral is ground bonded before the gfi, so the gfi is only looking for unbalance after that point.
So, here is an easy test:
Disconnect the reverse polarity indicator lamp.
Does the shore breaker still trip?
If not, then you've got a bona fide power reversal, and the light is tripping the gfi
Good luck!