I just purchased a Victory 6 Gang fused Switch Panel, with on/off lights for each circuit (part #AA10067). I've attached a photo of the backside of the panel.
My question is; can a 6 branch circuit (15 amps/ea, as per Victory packaging) panel be safely fed with 1- 16 awg conductor? I believe a 16 awg conductor max fuse rating is 25amps (21 in engine compartment).
Each branch circuit in the panel is fed with a 16 awg conductor, each having a max 15 amp fuse rating, which makes sense. What I can't get my head around is how the entire panel (6 circuits, 15 amp each) can be safely fed with 1 - 16 awg, 25 amp rated conductor.
If the loads were known and didn't exceed 25 amps, then the 16 awg feed may be acceptable.
What am I missing?
I just purchased a Victory 6 Gang fused Switch Panel, with on/off lights for each circuit (part #AA10067). I've attached a photo of the backside of the panel.
My question is; can a 6 branch circuit (15 amps/ea, as per Victory packaging) panel be safely fed with 1- 16 awg conductor? I believe a 16 awg conductor max fuse rating is 25amps (21 in engine compartment).
Each branch circuit in the panel is fed with a 16 awg conductor, each having a max 15 amp fuse rating, which makes sense. What I can't get my head around is how the entire panel (6 circuits, 15 amp each) can be safely fed with 1 - 16 awg, 25 amp rated conductor.
If the loads were known and didn't exceed 25 amps, then the 16 awg feed may be acceptable.
What am I missing?