Does anyone know if a Honda eu3000is will run the A/C on a 1993 Hunter 37.5? Thanks
 
Last edited:
Jun 2, 2004
5,802
Hunter 37-cutter, '79 41 23' 30"N 82 33' 20"W--------Huron, OH
It will if the unit is 16K btu or less. I can run my 12K Mermaid A/C with my 2000W Honda.
 
Nov 26, 2006
381
Hunter 31 1987 Fly Creek Marina Fairhope,AL.
Does anyone know if a Honda eu3000is will run the A/C on a 1993 Hunter 37.5? Thanks
It should run it fine if you do the math.

The gen set is 3000Watts.

To determine what the A/C requires, Simply use this formula.

AMPS x Voltage" usually 120Volts" = WATTS

So we have 2 of the 3 variables as follows.

3000/120=25 AMPS " current"
 
Sep 25, 2008
7,499
Alden 50 Sarasota, Florida
The critical element is the start or in-rush current requirement of the A/C unit. Without know which A/C you have, you really don't know for sure unless you find out, tell us or try it on a rental.
 
Mar 12, 2008
557
Jeanneau 49 DS San Pedro, CA
It should run it fine if you do the math.

The gen set is 3000Watts.

To determine what the A/C requires, Simply use this formula.

AMPS x Voltage" usually 120Volts" = WATTS

So we have 2 of the 3 variables as follows.

3000/120=25 AMPS " current"
Just keep in mind that the normal operating range of a generator is 75% of the rated maximum capacity. That drops the 25 amps down to about 19 amps.
 