During a recent survey, I received the following finding on my 2002 Hunter 356, "Under Generator power, every outlet shows reverse polarity. Ground neutral voltage is up around 31 volts. When the generator selector (circuit breaker) at the switch board is engaged the neutral and busses are supposed to be bonded together and the the neutral and ground busses ARE NOT supposed to be bonded together onboard when the selector is in the shore supplied power position." The boat has a Westerbeke 3.8KW generator installed.
Today I made measurements of the voltages at the AC Power Panels under the following conditions:
I have concerns about the fact that the polarity is inverted prior to switching on the generator breaker on the AC Panel, and that in general, the neutral to ground voltage is high and variable depending on load. I did not see negative polarity at the outlets, just a high ground to Neutral voltage.
Wondering if anyone has seen anything similar, or if this appears indicative of any issues. All the AC power loads appear to operate normally under generator power, but I do want to address this from a safety perspective..
Today I made measurements of the voltages at the AC Power Panels under the following conditions:
I have concerns about the fact that the polarity is inverted prior to switching on the generator breaker on the AC Panel, and that in general, the neutral to ground voltage is high and variable depending on load. I did not see negative polarity at the outlets, just a high ground to Neutral voltage.
Wondering if anyone has seen anything similar, or if this appears indicative of any issues. All the AC power loads appear to operate normally under generator power, but I do want to address this from a safety perspective..