I have a different circuit board & controller on my Dometic heat pump; however, I have chartered boats that have a Dometic system like yours. As others have mentioned, "HI" pressure codes can indicate restrictions in the raw water strainer & lines; ensure that the thru hull fitting doesn't have a plastic bag or seaweed blocking water flow. Also , blockage in the strainer & water line to the condenser can trigger a hi pressure fault code. The strainer can become clogged with algae, especially in summer months when the air conditioner is used more frequently. Also, realize that the controller can be programmed for the fan to run in two modes: (1) fan runs continuously at varying speed & condenser turns off when temperature set point is attained and condenser turns on again when temperature rises above set point. (2) fan & condenser turn off simultaneously when temperature set point is reached & both turn on again when temperature rises above the setpoint. You can set it in either mode depending on your preference.