A/B Diagnostics
Good input. You need to be organized about your detective work.
Here's a link to an online A/B manual:
http://www.fujiyachts.net/manuals/Adler-Barbour IO Manual.pdf
Another helpful source of parts:
http://www.rparts.com/
Another very helpful guy:
http://www.kollmann-marine.com/ He can and actually will talk you through it on the phone!
Fan -- if it's not running, check the wiring connections first. You can also check the fan integrity by disconnecting the wiring from the module and connecting to another power source, like two wires directly from the battery. If you need to replace the fan, it's $45 from a refrigeration supply house, but only $25 from Radio Shack: 4 inch 12 V DC fan #2730238. You'll need longer mounting machine screws since the fan is deeper.
Fuses: there's one right in the front of the module. 10A glass fuse, change it anyway while you're there, even if it looks good. My 1986 unit has a spare fuse in a plastic baggy right there!
Oil - you checked already. Unless your unit has been working worse and worse over a period of time, noticeably by having less cooling on the evaporator (in the fridge), then you would have had to have had a catastrophic failure of the seals on your connections or a pipe leak. That's good news that it looks fine.
NEVER change or mix refrigerants, don't let anyone ever try to talk you into it, it will NOT work. Rich found out the hard way. Also, never change just the compressor end without changing the tubing and evaporator, that won't work either - our local refrigeration guy told me that story, about how he caved into a customer, and ended up with an unhappy customer who conveniently "forgot" that he was the one who'd insisted on "saving $$" by only replacing the compressor! R12 is still available:
http://c34.org/bbs/index.php/topic,5084.0.html
Another good forensic story is here:
http://c34.org/bbs/index.php/topic,3259.0.htmlI don't think mixing refrigerants is a good idea.
Replacement electronic modules: ten years ago the WAECO guys knew their stuff, since then they've been bought and sold and I haven't heard any great reports that they've kept the guys who knew anything, but I could be wrong, so check with them.
Best way to TS is with a manifold gauge set --- If you have the proper connections, that is, you may not have them. See my C34 links for discussion.
There's a less expensive replacement module available from somewhere in Florida, I can't put my finger on it right now. Someone else here may know, I'll keep looking in my files.
15 A sounds very high. Normal run is 5A, runs about 50% of the time once it's cooled off inside the box, so that's where the 60 ah per day comes from for energy budgets. In fact 15A is nuts because the cold machines come with 10A fuses, unless your model 20A is way bigger than our cold machine, yours is 1987, ours is only a year older. Where have you been reading 15A?
You said:
we don't use it at the dock. These units are sensitive to low voltage. Is your house bank in good shape?? Have you tried the fridge with the shorepower connected and ON? What's the voltage at the fridge when it's not working?
Good luck, let us know what you found out, so we can keep up our forensic "library".