@FastOlson , the AC ground bus should be connected to the DC ground bus.
From ABYC E-11:
11.5.2.7 DC System Negative Connections
11 .5.2.7.1 If an alternating current (AC) system is installed, the main AC system grounding bus shall be connected to
11.5.2.7.1.1 the engine negative terminal or the DC main negative bus on grounded DC systems (see FIGURE 10) or
11 .5.2. 7 .1.2 the boat's DC grounding bus in installations using ungrounded DC electrical systems.
As @Davidasailor26 explained above, it's to ensure an efficient return to ground in case of a fault.
From ABYC E-11:
11.5.2.7 DC System Negative Connections
11 .5.2.7.1 If an alternating current (AC) system is installed, the main AC system grounding bus shall be connected to
11.5.2.7.1.1 the engine negative terminal or the DC main negative bus on grounded DC systems (see FIGURE 10) or
11 .5.2. 7 .1.2 the boat's DC grounding bus in installations using ungrounded DC electrical systems.
As @Davidasailor26 explained above, it's to ensure an efficient return to ground in case of a fault.