I direct you to Calder's book, page 146 in this case, and you'll see one example. While he diagrams 240 volts, the connectors on p147 are rated at 250 volts. I suggest everyone look to a reference book to find the truth, and not get replies that are 82 percent incorrect.
The nominal voltage, in the ranges used for small boat shore power wiring (and common single-phase wiring in buildings), is 120V and 240V nominal. Nominal as in 'name' - it is the official voltage designation in North America. The actual delivered voltage can drift around a bit, as there are tolerances on the 120/240V nominal as delivered from the utility, but that's how it's officially identified, and has been for a very long time.
110 and 220V is very old, and hasn't been the standard since well before I was born, though many folks, if not the majority, still use it in conversation. It's the nominal voltage in other countries, along with many others, but not around here.
Devices (receptacles, switches, etc.) are rated 125V and/or 250V. Look at any listed (UL, CSA, etc.) light switch, breaker (lighting and distribution, in land based applications), or receptacle, and you'll see 125V or 250V, or 125/250V. I don't know what the rating is for breakers intended for permanent installation on a boat, though.
In short:
125/250V - device rated voltage
120/240V - nominal voltage in North America, and usual non-motor utilization equipment voltage rating (like toasters and light bulbs)
115/230V - NEMA induction motor nameplate voltage rating (that would take another page to go into, but it's that way for a reason)
110/220V - obsolete in North America, but used by most folks in conversation. Also a common voltage in other countries, as is 50Hz power, though they're not necessarily related.
In the words of Michael Keaton, "220, 221; whatever it takes."
Edit: I haven't seen the page of Calder's book mentioned, but from the description given, Calder is correct in his useage of 240V in identifying the circuit, with devices (connectors) being 250V rated.