I am looking at the Victron screen that shows the dataHow are you measuring your State of Charge and loads? Is it possible that something is out of calibration there and either you’re starting at a lower SOC than 85%, or you’ve got some other loads that aren’t counted in the 200W?
I went through my system today and can’t see or think of anything that isn’t accounted for….Maybe you’re drawing more, have less than rated capacity, or not accounting for some other losses.
Victron must offer that feature.you should install a low voltage disconnect (LVD) so you don’t run them to flat zero (food is cheaper than lithium batteries).
Are you sure the Victron devices are set to the right bank size (400 AH)? If you’re going down to 0 overnight and getting back to 85% with solar that suggests you’re putting 4000 watt hours back into the bank over the day. That amount of recharging should only be possible with about 1000 watts of solar panels, which is a solar array usually only seen on multihulls. So either you’ve got more solar than I expect or your Victron equipment is underestimating your bank size, thereby judging that you’ve exhausted all your capacity before you really have, and put it much of it back in before you really did.I am looking at the Victron screen that shows the data
I guess I need a bigger battery bank then
What Victron screen? Do you have a shunt based monitor (BMV-712 or SmartShunt)? What solar controller? 99% of the time I see someone report a disparity between actual SOC and Victron reported SOC it is due to an improper “Charged voltage“ setting in the BMV/SmartShunt. The default setting doesn’t work with most solar charged systems. You should have the “Charged voltage“ set at 0.2V below the absorption voltage in the solar controller. Also if it is a Victron SmartSolar MPPT be sure to set up the ve.smart network and connect to the BMV/SmartShunt, if that’s what you have. This will ensure the MPPT compensates for voltage drop and doesn’t float early.I am looking at the Victron screen that shows the data
I guess I need a bigger battery bank then
Setting up a battery monitor correctly requires some effort and homework. Maine Sail has covered this, of course at Marine How To - DIY for Boaters - Marine How ToAll battery monitors do is to offer an educated guess as to state of charge. The programming of battery capacity, Puekert exponent, and charge efficiency variables all affect the accuracy of the guess.
This is correct. Also, you should not “float” lithium. Your charge controller should be set to stop charging after only about 5 minutes of reaching max charge.What Victron screen? Do you have a shunt based monitor (BMV-712 or SmartShunt)? What solar controller? 99% of the time I see someone report a disparity between actual SOC and Victron reported SOC it is due to an improper “Charged voltage“ setting in the BMV/SmartShunt. The default setting doesn’t work with most solar charged systems. You should have the “Charged voltage“ set at 0.2V below the absorption voltage in the solar controller. Also if it is a Victron SmartSolar MPPT be sure to set up the ve.smart network and connect to the BMV/SmartShunt, if that’s what you have. This will ensure the MPPT compensates for voltage drop and doesn’t float early.
Yep. My on the hook Solar float voltage is 13.4V which allows a small discharge… but I try to rarely get there. You can almost always take advantage of excess solar to do something. On shore power I usually set around 13.2V. As far as absorption time, there‘s a lot of competing advice there. I think Kilovault was 6 minutes. Lithionics is 30 minutes for balancing with a full charge recommended every 2 weeks. Victron says 2 hours per month, and Nordkyn design recommends tail current based on absorption voltage. When I use tail current the absorption time varies from 5-15 minutes.This is correct. Also, you should not “float” lithium. Your charge controller should be set to stop charging after only about 5 minutes of reaching max charge.
Victron monitors have a setting called 'discharge floor'. If its set to 50% (which is default i think) then the monitor would read zero if you discharged to 50% of the batteries capacity. I set mine to 0% so i always know exactly how much energy is still in my batteries but many people set it to 20% for lithium as that is the recommended depth of discharge for most lithium. I'm wondering if your settings are correct.hi all
I have 2x 200Ah Dakota litium batteries. The solar panel leave me at the beginning of the evening with 85% full
At night I draw 200w combined between ac and dc loads - fridge, freezer, fans.
Is that why I end up at 0%?
Thx!
The SOC calculation isn’t affected by the “Discharge floor”, so that shouldn‘t be his issue.Victron monitors have a setting called 'discharge floor'. If its set to 50% (which is default i think) then the monitor would read zero if you discharged to 50% of the batteries capacity. I set mine to 0% so i always know exactly how much energy is still in my batteries but many people set it to 20% for lithium as that is the recommended depth of discharge for most lithium. I'm wondering if your settings are correct.