Yes this would be the way it would be wired. So am I correct to assume you would be comfortable with using the 120A ACR in this system or would it be better off to spend the extra for the 500A? House bank does not go below 65-70% SOC before being charged. Yes it does have an external MC-614 regulator and hopefully it is getting programed correctly from all I have read from your post Maine Sail. Your information is greatly appreciated.
Yes the 120SI is more than enough IF the alt hits the HOUSE bank first. The 120A rating is a
continuous rating, it can handle up to 210A for 5 minutes. With a 100Ah start battery, and alt fed to house first, there is no way the ACR is carrying 120A, which would be a 1.2C charge rate of the start battery. Even if it could do this it would not last for any more than a few seconds and then only when the start battery was flat dead.
For someone who wires the ACR
incorrectly, with alt feeding to the start battery first, then yes the 120SI could be
marginal and you could eventually damage it. Of course you would also have other issues such as
relay-cycling due to the incorrect installation..
99.5% of the time your start battery will be pulling less than 20A across the relay, most often less than 3 - 4A..... The 500ML is a great device but is overkill here...