What size battery cable?

May 23, 2004
3,319
I'm in the market as were . Colonial Beach
I am wondering what size battery cable I should use for my system. Currently I am thinking 4 gauge, but I also wonder if 6 gauge would work.

My system will be pretty basic. My main battery draws are an TP10 Simirad Tiller Pilot, GPS, Depth, Stereo, 12 V fan (Camafro), LED anchor light, LED cabin light, and 1 regular cabin light. I rarely use running lights but they are regular bulbs too.

I am putting 2 6 volt batteries in a series. The run will go approximately 6 feet to a battery On/Off switch. It then will run about 6 feet back to a bus bar that will distribute the power to the fuse panels in the boat.

I am not running a lot of stuff in the boat. Is 4 gauge going to be overkill for the battery cables?
 
Sep 15, 2009
6,243
S2 9.2a Fairhope Al
for no/minimal difference in cost i would go 4 ga and fuse it to 150% of your expected load..or fuse it the rating for 4 ga are you going to controll all those things with breaker or switches
 
May 23, 2004
3,319
I'm in the market as were . Colonial Beach
Everything goes into a fuse panel. I would prefer breakers but, at this point, it was cost prohibitive.

It just seems like such a small load on the boat.
 
Sep 15, 2009
6,243
S2 9.2a Fairhope Al
i just checked prices and i see what you mean looks like for an 8 position panel with breakers it would run about 225.00 with led indicators
 
May 23, 2004
3,319
I'm in the market as were . Colonial Beach
Exactly. I have to use a horizontal panel in my boat and they are expensive. I will stick with the fuse panels and just keep extra fuses on hand.
 
Sep 15, 2009
6,243
S2 9.2a Fairhope Al
#6 will give you a 50 amp supply #4 will give you 80 amp supply so if you have no plans to grow later..... as Dave says #6 will be fine i would think
 

kito

.
Sep 13, 2012
2,011
1979 Hunter Cherubini 30 Clemmons
I am rewiring my ac and dc. I may have to rethink this. I have 4 ga from bat to bat switch and was going to run 2 10ga wires off the switch, one to each panel. One panel is only 2 foot away and the other is about 6 foot. I reck'n I thought I would never have all my dc on at the same time but you never know. I better go with 2 8 ga wires to be safe.
 
Jun 8, 2004
10,376
-na -NA Anywhere USA
battery cable concerns for DC is different for the wire used in AC as you would want to use a marine grade 12-3. Do not use the cable purchased from Lowes or Home depot as you are around water. The marine grade for AC 12-3 is more flexible and double sheathed. As for the DC or 12 volt, the use of yellow coated wire for negative ground is recommended to avoid confusion of the hot side of AC 12-3 which is black. Knew too many batteries blown up with black hot side of AC 12-3 attached to negative battery terminals.
 

kito

.
Sep 13, 2012
2,011
1979 Hunter Cherubini 30 Clemmons
Thanks for the tip Dave. I was going to place an order for 100 feet of black tinned copper wire tomorrow but will change to yellow instead.
 
May 23, 2004
3,319
I'm in the market as were . Colonial Beach
twalker260...That is awesome news and a good idea. I may have to look into that. The price seams reasonable. Is there any downside to this?
 
May 23, 2004
3,319
I'm in the market as were . Colonial Beach
What size should I use? I am not sure right now, and not at the boat, of the size of the fuse that I have in these. I am thinking 15amp breaker?
 
Feb 26, 2004
22,986
Catalina 34 224 Maple Bay, BC, Canada
What size should I use? I am not sure right now, and not at the boat, of the size of the fuse that I have in these. I am thinking 15amp breaker?
BO, not sure with all this input why you are still asking. The "size of the fuse" where? On the batteries? Maine Sail has discussed this many times. It depends on the size of the wire you choose.

I am sure you've developed a wiring diagram before you start the wiring, right?:)

Charlie Wing's books is very good on this stuff. It used to be available on scribd, but they took it down. PM me and I'll send it to you in a PDF.
 
Dec 2, 2003
764
Hunter 260 winnipeg, Manitoba
Fuse size is usually determined by the size of wire that it is protecting - unless it is protecting a specific piece of equipment (which is of lower amperage than the wire size would need to protect it)

You should be fairly safe to simply determine the rating of the current fuse and replace with a comparably rated resettable breaker.

Here is a link to an very good chart to determine the required fuse ratings on different wires in different situations.

http://assets.bluesea.com/files/resources/reference/20010.pdf

You could also have a look at wiring diagrams in current vessels to get a rough feel of what is used in different applications.

Should mention that these breakers are what was used on our 2004 oem panel.
No real downsides that I'm aware of - and you don't have to have a handful of spare fuses rolling around somewhere that you can't find or you have the wrong size!