In less than 6 hours it brought up the levels considerably. I think this might be a winner.
Robert,
Try not to confuse voltage rise with a capacity increase. In order to get current flowing into a battery you need to increase the voltage. A voltage increase while charging is not representative of state of charge until you can hit and hold an absorption voltage for a while. If you are at absorption voltage (roughly 14.4V) you can safely guess that you're at close to 80% state of charge or higher. This is with healty batteries. Batteries suffering from sulfation will come up to 14.4V well before they are actually at 80% SOC and this is then misleading. If you have an inexpensive shunting controller then the last 20% of charge will take a loooooong, loooong time regardless of sun.
A 15W panel will pump out about 0.9A for 3 - 4.5 hours per day, roughly. This is also with no shading. So if we figure 0.9 X 4 hours this = 3.6Ah per day of charging.
With a 100Ah battery at 50% state of charge 50 Ah's, plus about 15% charge inefficiency, would need to be replaced or 50Ah X 1.15 = 57.5Ah.
57.5Ah / 3.6Ah per day = 16 days to get a single 100Ah battery from half full to full, in perfect conditions with a 15W panel.
A 200 Ah bank would take approx 32 days to reach full, from half full...... These are averages and you may do slightly better and you very well can do considerably worse. A 15W panel is really in the "maintenance" realm of maintaining a charge not necessarily charging/replacing it quickly or in a timely fashion.
It your OB motor can get the bank back to 80% state of charge regularly then base these figures on 20% of the capacity.
A 100Ah battery at 80% SOC - 20 Ah X 1.15 = 23 Ah / 3.6 =6.4 days to go from 80% to 100% in perfect conditions.