Amp/Feet
My comments on using a “common” negative wire were incomplete.I recommend using a discrete Negative wire for each Positive - the wires being the same size. Sometimes, especially when 2 (or more) circuits will NOT likely be “on” at the same time, you can combine two circuit Negatives on a single “common” Negative. It’s usually prudent to “upsize” a common negative, to accommodate a potential emergency situation where both circuits are “on” simultaneously. In this case, the Negative wire size should be calculated for the combined load of both circuits.I have prepared a little chart which includes pre-calculated figures for required wire sizes for Amp/Feet of circuit (at 3% Voltage Drop), and other useful information required for for circuit design. Send me a FAX number, and I’ll fax a copy to anyone interested.Gord@BoatPro.zzn dot comIe:For maximum 3% Voltage Drop @ 12 Volt#12 AWG Copper wire ~ 150 A/Ft #10 AWG ~ 300 A/Ft#8 AWG ~ 450 A/Ft#6 AWG ~ 900 A/Ft#4 AWG ~ 1,250 A/Ft#2 AWG ~ 2,200 A/Ft#1/0 AWG ~ 3,500 A/Ftetc.An Amp/Foot is 1 Amp over a distance of 1 Foot (return circuit length = Pos + Neg lengths)Hence:20 Watts @ 12.75 V = 1.57 Amps (actually 1.5686 A)1.5686 A x 100 Ft = 156.86 A/FtFrom the chart, #12 AWG is only suitable for 150 A/Ft - so I very slightly undersized my previous example - could have selected the next higher wire size - #10 @ 300 A/Ft, and perhaps #8 for common negative (requires 314 A/Ft). More info’ on the CruiserForum.comFWIW,Gord