Hi Guys,
I thought posting here again since I got so good advice last time. This time, it's about batteries and inverters.
I have inside the house bank 3 x Bosch N120 (120AH, calcium-calcium) batteries. They are 12V and connected in parallel.
These are connected to a Victron Multiplus Compact 1600 (1600/70/16) inverter charger.
I want to run a microwave that takes around 1100 Watts (measured).
I did not choose the batteries, they are what came with the boat (they are fairly new, at around 1 year old). I did choose the Victron because I had a Victron on my old boat and was quite happy with it (also I like the footprint)
I do have a genset I can run the microwave off, but ideally it would be nice if I can heat up something quickly without putting cold hours on it.
However here is the result:
I turn on the microwave, and it would run for around 2-3 seconds, then the battery would drop to 11.3 on the panel and the inverter control panel would yield low battery & overload simultaneously (which the victron handbook says means that the 12V supplied are not stable - they talk about a ripple voltage which is too high)
I turn the system off immediately, the voltage on the panel returns to 12.6 (or whatever it has been before) and after a thinking phase (on part of the charger I guess) the system starts recharging the batteries which finishes within seconds.
I have a bank of 4320 w/h and if I use around 1100 * 5/60 (5 minutes warming up time) it should use around 10Ah of my bank (360Ah) which seems OK to me.
Also, since I have three batteries, I would think that each of them would contribute around 33.33A (1100 Watt load is 92A so let's say with inverter inefficiency that's 100Amps) According to what I can find on the internet they should last for 245 minutes on 25 Amps.
Shouldn't this work?
What's the most likely reason this doesn't work. Do you think it lies in the batteries? The Victron is rated for 1600W continuous load.
Voltage on the electric panel drops to 11.3 Volts while the magnetron is on, what do you make of this (other than, obviously, high load)
Am I expecting too much or is it just bad equipment for the job?
Cheers and thanks,
Tom
I thought posting here again since I got so good advice last time. This time, it's about batteries and inverters.
I have inside the house bank 3 x Bosch N120 (120AH, calcium-calcium) batteries. They are 12V and connected in parallel.
These are connected to a Victron Multiplus Compact 1600 (1600/70/16) inverter charger.
I want to run a microwave that takes around 1100 Watts (measured).
I did not choose the batteries, they are what came with the boat (they are fairly new, at around 1 year old). I did choose the Victron because I had a Victron on my old boat and was quite happy with it (also I like the footprint)
I do have a genset I can run the microwave off, but ideally it would be nice if I can heat up something quickly without putting cold hours on it.
However here is the result:
I turn on the microwave, and it would run for around 2-3 seconds, then the battery would drop to 11.3 on the panel and the inverter control panel would yield low battery & overload simultaneously (which the victron handbook says means that the 12V supplied are not stable - they talk about a ripple voltage which is too high)
I turn the system off immediately, the voltage on the panel returns to 12.6 (or whatever it has been before) and after a thinking phase (on part of the charger I guess) the system starts recharging the batteries which finishes within seconds.
I have a bank of 4320 w/h and if I use around 1100 * 5/60 (5 minutes warming up time) it should use around 10Ah of my bank (360Ah) which seems OK to me.
Also, since I have three batteries, I would think that each of them would contribute around 33.33A (1100 Watt load is 92A so let's say with inverter inefficiency that's 100Amps) According to what I can find on the internet they should last for 245 minutes on 25 Amps.
Shouldn't this work?
What's the most likely reason this doesn't work. Do you think it lies in the batteries? The Victron is rated for 1600W continuous load.
Voltage on the electric panel drops to 11.3 Volts while the magnetron is on, what do you make of this (other than, obviously, high load)
Am I expecting too much or is it just bad equipment for the job?
Cheers and thanks,
Tom