I powered my 12000BTU aircon with Elemax(Engel) SHX2000 Genset. It runs ok. Out of curiousity, I fitted the Supco Hard Start Kit SPP6 across the Run Cap (as advised by Supco) but the aircon compressor won't run.
Shouldn't the Hard Start Kit be across the Start Cap instead? Any idea?
 
Feb 26, 2009
716
Oday 30 Anchor Yacht Club, Bristol PA
Take it off, If your unit has a start cap it already has hard start wiring.
 
Feb 26, 2004
22,979
Catalina 34 224 Maple Bay, BC, Canada
I mistakenly, perhaps, thought this was a soft start for a hard-to-start AC unit. :) Did I get my terminology backwards? Wouldn't be the first time...
 
Nov 19, 2011
1,489
MacGregor 26S Hampton, VA
A hard start (super boost) goes on the run cap, but since you already have a start cap, you may want to check it to make sure it's good.
 