Some things to consider:
#1 All hose connections need to be made inside the propane locker. If no locker than propane gasses must not be able to get into the boat eg: what Greg has done...
#2 If adding a heater the hose and terminations must be run to the locker and all connections made inside the locker.
#3 Consider a propane sniffer than also breaks the solenoid. Test the sniffer bi-monthly with a butane lighter by just pressing the gas not the flame.
#4 I personally prefer a solenoid for each device rather than one for the manifold for two or more devices.. A positive shut off is required from the appliance area and the solenoid is the easiest way to go about this.
#5 You should have a means of shut off within reach of the cook stove without reaching over it in the event of a flame. If your DC panel is close than this can work.
#6 I prefer to see a bright red LED light indicating propane is on.
#7 The regulators and gauges from Trident are perfectly fine and will have factory made connections if you are not comfortable making them yourself.
#8 I prefer that solenoid because they are VERY reliable and can go in front of the regulator or after where most need to go after.. I have seen regulators rot out. No sense in having a shut off after the leaking regulator...
Below are some key points from ABYC A-1:
"1.7.2 Each appliance shall be served by a separate low pressure, i.e., 14 in. water column (3.5 kPa), regulated supply line that shall originate inside the cylinder locker or protective enclosure.
1.7.3 A readily accessible manual or electrically operated (e.g., solenoid) shut-off valve shall be installed in the low or high-pressure line at the fuel supply. See the requirements in
A-1.7.6.1 for valve location requirements.
1.7.3.1 The valve(s) or its control must be operable in the vicinity of the appliance(s) in the event of a fire at any appliance(s). If the cylinder shut-off valve is readily accessible from the vicinity of the appliance, the shut-off valve on the supply line is not required.
1.7.3.1.1 The valve or its control shall be operable without reaching over the top of any open flame appliance, e.g., cooking appliance burners.
1.8 LPG LOCKERS
1.8.1 Lockers used to contain LPG cylinders, cylinder valves, regulating equipment and safety devices shall be designed to minimize the likelihood of use as a gear storage locker and shall be
1.8.1.1 vapor tight to the hull interior, and
1.8.1.2 located above the waterline, and
1.8.1.3 constructed of, or lined with, corrosion resistant materials, and
1.8.1.4 shall open only from the top with a gasketed cover that shall latch tightly, and
1.8.1.5 shall be capable of being quickly and conveniently opened without tools.
1.8.2 Installation
1.8.2.1 LPG lockers shall be installed so that the locker opens only directly to the outside atmosphere, and
1.8.2.2 if a LPG locker is installed inside a boat locker, the LPG locker shall be located as high and as close to the boat locker’s opening as possible in order to comply with A-1.8.2.1.
1.8.3 When means of access to the LPG equipment locker or housing is open, the cylinder valves shall be capable of being conveniently and quickly operated, and the system pressure gauge dials shall be fully visible.
1.8.4 Lockers shall be vented at the bottom by a dedicated vent, with a minimum diameter of any component in the vent system that shall be not less than 1/2 inch (12.7mm) inside diameter.
1.9.2 LPG fuel supply line shall comply with the construction, performance, manufacturing and production test, and marking requirements of UL 21, LP Gas Hose
Locker vents shall be led outboard, without pockets, through the hull to a point lower than the locker bottom and above the waterline with the boat in the static floating position.
NOTE: See ABYC H-27 Seacocks, Thru-Hull Connections and Drain Plugs for requirements for seacocks.
1.8.6 Locker vent openings shall be located at least 20 inches (508 mm) from any hull opening to the boat interior.
1.8.7 LPG lockers shall not be used for storage of any equipment other than LPG cylinders, cylinder valves, regulating equipment, and LPG safety devices. See A-1.8.1.
1.8.8 Storage provisions for unconnected reserve cylinders, filled or empty, shall be the same as for the cylinder in use.
1.9.3 Flexible LPG supply line shall be equipped with permanently attached end fittings, such as a swaged sleeve or sleeve and threaded insert.
1.9.5 Fuel Line Location and Installation
1.9.5.1 Fuel supply lines shall be protected from physical damage, and
1.9.5.1.1 shall be accessible for inspection.
1.9.5.2 A flexible LPG fuel line section shall be used to allow free swing of gimbaled stoves.
1.9.5.3 Fuel supply lines shall be supported by clips or straps or other suitable means such as conduit or tray to prevent vibration damage, and
1.9.5.3.1 the clips or straps or other devices shall be corrosion resistant, and
1.9.5.3.2 shall be designed to prevent cutting, abrading, or damage to the lines, and
1.9.5.3.3 shall be galvanically compatible with fuel supply line material.
1.9.5.4 Fuel supply lines shall be protected by close fitting grommets, sleeves, or sealant of non-abrasive material wherever they pass through decks or watertight bulkheads, and the method used shall be watertight.
1.9.5.5 Fuel supply lines passing through bulkheads that need not be watertight shall be installed so that the bulkheads will not cut, abrade, or damage the line.
1.9.5.6 Fuel supply lines shall be continuous lengths of tubing, piping, or hose from the regulating device, solenoid valve, or leak detector to the appliance, or to the flexible section at the appliance."
Be SAFE!