I have installed a 140 amp Electromaxx alternator on my Yanmar 3YM30. The
2/0 cables to the battery selector from the 420 amp hour AGM house battery
bank and the 200 amp hour AGM starter battery are both currently protected
with 300 amp class T fuses within 7” of each battery positive terminal. The
wire runs from battery selector to starter are also 2/0. The negative
cables are all also 2/0.
The + wire from the alternator to starter is 2ga with 18 inch length.
The round trip length from the starter to selector switch
and on to the batteries is 50’ so at 14.2V and 100 amps I expect about a
2.7% voltage drop with 2/0 cable.
I will be installing a Balmar MC-614-H external regulator with temperature
sensors for both batteries and alternator.
I normally set the selector switch to “both” and discharge and charge the
battery banks simultaneously.
My understanding from reading much of the information is that I need to fuse
the wire run from alt to starter or the 15 feet from starter to battery
selector, which of course runs to battery banks.
Questions:
1) Should I put a fuse between the alternator and the starter or between
the starter and selector switch ?
2) Which is the best kind of protection (Class T, ANL, ANN) for the wire
from the alternator ?
I am confused how to protect the alternator from being damaged when the
protection fuse is blown in the alternator-starter-battery switch run.
Is it suggested that a zap-stop (zener diode) protection is used on +
alternator output?
Will a single zap-stop be able to sink the 140amp/14V (~1.9kWatts) output
for a second without failing?
The “new” Balmar TSP (transient spike protection) device looks to be the
same as the “old” zap-stop but with a fuse in line. If the TSP is trying to
sink 1.9kW won’t that poor old fuse blow and defeat the purpose of the TSP,
which is to provide a path to ground for the un-dissipated energy in the
spinning alternator?
2/0 cables to the battery selector from the 420 amp hour AGM house battery
bank and the 200 amp hour AGM starter battery are both currently protected
with 300 amp class T fuses within 7” of each battery positive terminal. The
wire runs from battery selector to starter are also 2/0. The negative
cables are all also 2/0.
The + wire from the alternator to starter is 2ga with 18 inch length.
The round trip length from the starter to selector switch
and on to the batteries is 50’ so at 14.2V and 100 amps I expect about a
2.7% voltage drop with 2/0 cable.
I will be installing a Balmar MC-614-H external regulator with temperature
sensors for both batteries and alternator.
I normally set the selector switch to “both” and discharge and charge the
battery banks simultaneously.
My understanding from reading much of the information is that I need to fuse
the wire run from alt to starter or the 15 feet from starter to battery
selector, which of course runs to battery banks.
Questions:
1) Should I put a fuse between the alternator and the starter or between
the starter and selector switch ?
2) Which is the best kind of protection (Class T, ANL, ANN) for the wire
from the alternator ?
I am confused how to protect the alternator from being damaged when the
protection fuse is blown in the alternator-starter-battery switch run.
Is it suggested that a zap-stop (zener diode) protection is used on +
alternator output?
Will a single zap-stop be able to sink the 140amp/14V (~1.9kWatts) output
for a second without failing?
The “new” Balmar TSP (transient spike protection) device looks to be the
same as the “old” zap-stop but with a fuse in line. If the TSP is trying to
sink 1.9kW won’t that poor old fuse blow and defeat the purpose of the TSP,
which is to provide a path to ground for the un-dissipated energy in the
spinning alternator?