Greetings all!
I am considering adding to my current 40A ProTech4 shore power charger a new 50A ProNautic 1250, and using both chargers on my 390Ah lead acid house bank when charging via generator power.
Why do I want more charging capacity? I have both a fridge and a freezer, and when you add their power consumption when running (6A + 6A) plus a few amps of house loads (maybe 3A), there's not much left to charge my batteries (40A - 6 - 6 - 3 = about 25A actually feeding the house bank). I've confirmed this with my battery monitor. When plugged in at the dock it doesn't matter since I've got all night. When anchoring out, though, replenishing even 75 or 100 Ah takes a while. I don't like disturbing the peace more than I have to even though my generator is pretty quiet.
My proposed two charger configuration could provide 90A of power, where effectively 75A would flow into a discharged house bank... tripling my charging rate. 75A is also still below the 20 or 25% max charge rate I could realistically expect from a 400Ah lead acid house bank.
So my question is, can I run two chargers into the same house bank at the same time? I expect both would run in "bulk" mode until the charger with the lowest preset voltage changed to "acceptance," at which time the other charger would gradually take over the remainder of the charging.
I realize it would be simpler to just have ONE big shore power charger, but that also costs lots more since my existing charger still works. I kinda like the possible redundancy this configuration could offer as well.
I think each charger would have its own switch on the AC panel, so I could easily control the charge rate of the batteries.
Am I crazy? Or is does this sound like a good idea? Thanks!
I am considering adding to my current 40A ProTech4 shore power charger a new 50A ProNautic 1250, and using both chargers on my 390Ah lead acid house bank when charging via generator power.
Why do I want more charging capacity? I have both a fridge and a freezer, and when you add their power consumption when running (6A + 6A) plus a few amps of house loads (maybe 3A), there's not much left to charge my batteries (40A - 6 - 6 - 3 = about 25A actually feeding the house bank). I've confirmed this with my battery monitor. When plugged in at the dock it doesn't matter since I've got all night. When anchoring out, though, replenishing even 75 or 100 Ah takes a while. I don't like disturbing the peace more than I have to even though my generator is pretty quiet.
My proposed two charger configuration could provide 90A of power, where effectively 75A would flow into a discharged house bank... tripling my charging rate. 75A is also still below the 20 or 25% max charge rate I could realistically expect from a 400Ah lead acid house bank.
So my question is, can I run two chargers into the same house bank at the same time? I expect both would run in "bulk" mode until the charger with the lowest preset voltage changed to "acceptance," at which time the other charger would gradually take over the remainder of the charging.
I realize it would be simpler to just have ONE big shore power charger, but that also costs lots more since my existing charger still works. I kinda like the possible redundancy this configuration could offer as well.
I think each charger would have its own switch on the AC panel, so I could easily control the charge rate of the batteries.
Am I crazy? Or is does this sound like a good idea? Thanks!