I was looking for the wiring from the panels to the controller.. Are you asking round trip, panels from the panel to the controller and back to the panel, that measurement would? If so that would be 54'.
In DC wiring the wire distance is always the round trip, the length of the positive and negative wires, in your case from the panel to the controller an back again.
The Panel produces about 6 amps at 61v under load and 6 amps at 81v open circuit. Using the
ABYC Ampacity chart 18ga Marine wire rated at 105°c wire can handle 20 amps. So in theory, you could use wire that small. In practice, it would be nuts to do that.
The Blue Sea Voltage drop calculator does not give the option for 80v or even 60v. The closest the Blue Sea calculator can get is 15a @ 32v which is 480w. The calculator says 10ga for a 3% loss. You should be fine with 10ga.
The reason this works, is wire is rated for amps, not watts. The higher the voltage the lower the amps required to get the same wattage. The math is simple for DC, volts * amps = watts. With higher volts smaller diameter wires are required.
The controller will take the high voltage low amperage current and convert it to low voltage high amperage current. So it will be necessary for the installer to calculate the wire sized from the controller to the battery.