Some considerations from the ABYC:
From A-26
26.5.1 LPG and CNG fueled appliances shall not be installed in spaces containing internal combustion engines,their fuel tanks, or joints and fittings of their fuel systems.
26.5.3 Appliances shall meet the combustion requirements of ANSI Z 21.57 Recreational Vehicle Cooking Gas Appliances.
26.5.4 Printed instructions for proper installation, including air intake and exhaust systems, operation, and maintenance shall be provided with each appliance.
26.5.4.1 The instructions shall include information on the risks associated with the air consumption of the appliance, and
26.5.4.1.1 venting of combustion products from the appliance.
26.5.5 A burner system shall be capable of operation without creating a fire hazard during periods of boat pitch and roll, at angles up to 30° from horizontal in any direction, and continuous operation at angles of heel up to 30°.
26.5.6 Operating controls shall be located to be easily accessible, and to minimize possible injury from burners or elements when being used.
26.5.7 Appliance controls shall be designed to require a push-turn or other two phase operation when going from “off” to “on” position.
26.5.8 The design and installation of LPG and CNG appliances and systems shall provide for the consumption of air and the venting of exhaust products.
26.5.9 Pilot lights and other automatic ignition devices shall be permitted only in appliances with room sealed combustion systems.
26.5.10 Unattended appliances shall incorporate a room sealed combustion system.
26.5.11 Attended non-room sealed combustion system appliances shall be equipped with an oxygen depletion sensor that cuts off the fuel supply to the appliance when the room oxygen level falls below 95% of normal, and/or failure of oxygen depletion sensor.
26.5.11.1 In addition to the oxygen depletion sensor, the manufacturer of the appliance shall provide a warning label to alert the appliance operator to maintain adequate ventilation during appliance operation.
26.5.12 All appliances shall have flame failure devices on all burners, and pilot lights, that will prevent gas from flowing to the burner if flame is not present.
26.5.13 When operating at the rated capacity, the exterior surfaces of the appliance shall not exceed 180°F (82°C) when tested in an ambient temperature of 77°F (25°C), and
26.5.13.1 the appliance shall be designed so that, when installed, the temperature of the surface below, and
immediately surrounding vertical combustible surfaces, shall not rise more than 150°F (65°C) above the compartment’s ambient temperature.
26.5.14 Appliances shall be mounted in accordance with the manufacturer's instructions and in accordance with this
standard.
26.6.1 Exhaust products shall be ducted to the exterior of the vessel and designed to minimize water entry, back draft, and exhaust re-entry through any hull openings, ventilators, opening ports, hatches, windows.
26.6.2 Flues shall be routed and sized to ensure complete discharge of the products of combustion outside the craft, and shall not be obstructed by an accumulation of water.
26.6.2.1 The flue system shall be continuous and sealed from the appliance to its terminus outside the craft.
26.6.2.2 Flue terminus shall not be positioned within 20 inches (500mm) of a refueling fitting or fuel tank vent.
27.6.2.3 Dampers, i.e., shut-off valves, shall not be installed in flue systems.
27.6.2.4 The flue system shall be accessible for inspection.
26.6.2.5 Exposed surfaces of flues, smoke pipes, or stacks in accommodation spaces shall not have a surface temperature greater than 180°F (82°C) during operation with a compartment ambient temperature of 77°F (25°C).
26.6.3 Double or triple wall smoke stacks shall meet the requirements of UL 103 Chimneys, Factory-built, and shall be installed in accordance with the instructions of the manufacturer.
Definitions:
Unattended Appliance - appliances intended to function without frequent attention by an operator, and that may cycle
on and off automatically, such as refrigerators, thermostatically controlled cabin heaters, and water heaters.
Room Sealed Combustion System - a combustion system in which incoming air, the combustion chamber, and the
outgoing products of combustion are sealed from the boat interior.