( from Stu): I recommend that it be replaced with either a single or double pole breaker, with the ground directly connected, i.e., NOT on or through a breaker. The double pole (hot and neutral) breakers are required by the newer AYBC Code. Single pole breakers (on the hot [back 120V] leg) were fine for many years earlier. Since Blitz obviously has room behind his panel for a multiple-bank breaker, he should use the newer two pole breaker. The double pole breakers are NOT linked, that's why there are two "handles" and both need to be moved, one can be moved and the other will stay where it is unless moved by hand - that's why there are two of them there.
Stu, thanks for the research. I know it's time consuming. I should be down vacuuming the sawdust out of the boat from the last two projects, but here I sit at the keyboard.... The AC main MUST be a double-pole type, according to ABYC, and the double-pole breakers for AC mains need to be linked. In the Blue Sea electrical catalog, every AC main breaker they have shows the toggles linked so they MUST be operated at the same time. If using two individual breakers, a bolt through the toggles will do the same thing. If either breaker trips, it will shut the other one off with it. Correct on the ground- never disrupt it!
Stu, thanks for the research. I know it's time consuming. I should be down vacuuming the sawdust out of the boat from the last two projects, but here I sit at the keyboard.... The AC main MUST be a double-pole type, according to ABYC, and the double-pole breakers for AC mains need to be linked. In the Blue Sea electrical catalog, every AC main breaker they have shows the toggles linked so they MUST be operated at the same time. If using two individual breakers, a bolt through the toggles will do the same thing. If either breaker trips, it will shut the other one off with it. Correct on the ground- never disrupt it!