Due to the properties of the refrigerant, as you lower the evaporator (suction) pressure, the refrigerant boils at a lower temperature (also true of water - which can be used as refrigerant if you're up to a challenge). At any rate, as refrigerant leaks out of a system, the pressures in the system go down. When enough refrigerant leaks out, you flash it all right where it is introduced into the coil. This creates a small zone of very cold metal which freezes the condensate from the air. As this frosts over, it lowers the heat transfer in that section, allowing the frost boundary to continue to progress across the coil until the capacity of the charge won't go any further. Depending on the conditions, it might just be one section, or might turn the whole thing into a block of ice.
The irony is, the system isn't cooling as well due to the low charge, but parts of it are freezing.
You can catch the problem if you constantly monitor your supply air temperature while the system is operating in steady state. The overall supply air temperature will go up as your charge decays. If your typical discharge temp at the closest register is 53 deg; then one day you notice it doesn't get below 62 deg, your charge is on its way down. This observation needs to be made when the conditioned space is at roughly consistent temperatures. In the southeast, or other humid areas, the indoor humidity will start to rise, also; making the house less comfortable even if its holding temperature. You are cooling only in one section of the coil. The air that's not running through that section gets very little cooling effect. And yes, I actually am so much of a geek that I monitor my discharge air supply temp.
While one of my certifications is refrigeration mechanic, I don't have experience with this particular unit. So, when you guys that own one say they all freeze, or have defrost cycles, I'm not arguing with you. I'm just saying that in most of the systems I'm familiar with; if the coil is freezing, it's either airflow or refrigerant charge.
There is one other possibility that we should consider. How cold was the condenser water?
I assumed that the unit ran fine in the past and this is something new. True?